Baseboard Heat
Why does the sound of baseboard heat change when the circulating water gets hot? Is it due to pressure increase on the pump?
Comments
-
Can you be more specific about "the sound". Give some descriptive words about the sound changes and be more specific about the timing of the circulator, the boiler start and the specific type of baseboard (fin tube or cast iron).
0 -
Fin tube baseboard. Sounds like a whirling sound probably from pump when boiler starts up, but gets quieter when the hot water starts circulating.
0 -
Thanks. Metal sounds link "tinkling/crinkling/ticking" are heat-expansion. "Gurgling and whirling" water sounds are usually air or bubbles in the system. The bubbles/air "gather" in resting places when the water isn't moving, then they scatter and spread out when the circulator starts and make noise. Check the status of your air elimination devices and the "health" of your expansion tank. Check your system pressure on the gauge when it is running and resting. Make sure there are no leaks on the system.
0 -
Corr: Metal sounds like….
0 -
thanks
0 -
An oversized pump can create hissing or whirling type noise
It could diminish as additional zones open up
Is this a newly developed sound? Has changed in the system?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The sound changes because the velocity increases due to the heating of the water. Hot water is less viscous than cold water so it flows easier, albeit, faster with the same pressure. This is why I adjust my balancing valves at operating temperature.
0 -
is your circ before or after the expansion tank?
known to beat dead horses0 -
You sure it's related to the hot water? Do you have a Mod/con boiler? if you have a Mod/con the boiler the sound may be decreasing due to the water getting closer to the set point temperature so the ECM motor is slowing down in a effort to reduce the BTU input. You might be hearing the ECM motor slowing down. You really shouldn't be hearing water flowing thru your baseboard.
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements