  • ethicalpaul
    ethicalpaul Member Posts: 8,850
    edited March 21

    Huh, steam burns from a boiler releasing all of its 180 degree water, got it! CBS news has really taken a turn for the worse for some reason!

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 16,890
    edited March 21

    it wasn't 180, something happened causing the controls to runaway or it was actually a steam system, the water was superheated, when it returned to atmospheric pressure it flashed to steam and it likely had a faulty or missing relief valve(although under some circumstances just the relief valve opening could be pretty violent).

    they barely have the resources to report the story much less research the intricacies of boiler accidents. the only part i fault them for is that instead of saying nothing they used some sort of "ai" tool that gave them fictional information.

    at some point there will be an engineering report on what happened.

    hopefully it isn't like the repot on the block that blew up in flint that was essentially you aren't important enough to bring in the right experts to figure out exactly what gas thing failed.

    ethicalpaul
  • jesmed1
    jesmed1 Member Posts: 1,481
    edited March 23

    Later reports say it was a large hot water holding tank, not a boiler, that ruptured. From the extensive damage it does look like an overpressure event.

    https://foxbaltimore.com/news/local/people-injured-explosion-building-collapse-carroll-county-greenhouse-facility

    Oddly, Googling "Maryland boiler explosion" also got me the link below to an actual boiler "explosion" that happened last fall in a Baltimore police station. It looks like the front of the boiler got blown off, maybe from gas leak/delayed ignition.

    https://www.thebanner.com/community/local-news/white-marsh-explosion-police-boiler-GZMIM5VLIVCJ5GRQZTAV57FQDE/

  • Steamhead
    Steamhead Member Posts: 18,525
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    jesmed1
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,228

    Relief or safety valve rusted closed and or plugged with a pipe plug+ some control ran away.