heat load calc
Hi fellas. So after 10 years of being employed I decided to start my own business. I,m bidding a house in central NY. I ran my numbers through CoolCalc and my losses came out to 44,000 needed for cooling. 42,000 needed for heating. Theres a lot of windows but unless i screwed up, it seems like a lot of cooling needed. I did room by room, and I'd think the heat loss would be greater than the heat gain. Any advice ? its a 2 story 1300 square foot house on Cayuga Lake near Ithaca NY. Thank you guys.
    EdTheHeaterMan Member Posts: 12,147
    Infiltration is the thing that can make your number go way off. How many air changes per hour are you including in the calculation? if it is a 100 year old barn, then 2 to 3 air changes per hour will may your system size almost 150% larger that the same size home built in the 2000's where all the insulation and weather sealing offers you less than 1/2 an air change per hour.
    mattmia2 Member Posts: 16,733
    unless you have something very unusual happening there is a problem with the heat loss software you used or the information you gave it. in an area with an ~70 f degree heating delta and ~20 f degree cooling delta the heat loss and heat gain should not be nearly identical.
    EBEBRATT-Ed Member Posts: 20,163
    Rule of thumb in the NE is that usually with the average house the cooling load is roughly 1/2 the heating load. But things vary.
    the heat loss seems plausible for a structure that size in that climate. The gain seems wildly oversized. maybe look for something that has made the solar gain calculations go crazy. does it itemize out how it got its numbers?
    hot_rod Member Posts: 27,445
    if it is new construction I would expect a 1300 sq ft home to be under 20 btu/ft. So more like 25-30,000 btu/ hr load
    But if it is on the lake with big glass the load increase. Heating and cooling
  • Christalli52
    Christalli52 Member Posts: 3
    Agree with you all so far. brand new home being built with spray foam and r 50 in the attic. fiberglass i think. Anyone use coolcalc? Or have a suggestion?
  • Christalli52
    any suggestion for air exchange? I'd like to have one an hour, or run it off of carbon monoxide.
  • neilc
    neilc Member Posts: 3,174
    Dioxide ?
    known to beat dead horses
    mattmia2SuperTech
    Tight construction like that will not get 1 change per hour. You will need to do that mechanically and I would do it with and HRV or ERV in order to get that number above 1 or more
    mattmia2GGross