Options
wcs5050
wcs5050 Member Posts: 177
edited 12:42AM in THE MAIN WALL

I’ve seen this here and there, and utilized the method a couple times. It now occurs to me that these stainless braided connectors may not be oxygen barrier… obviously not intended for this purpose. Anyone have a preferred connector this?

Comments

  • HydronicMike
    HydronicMike Member Posts: 336

    Why would you want it flexible.
    Ive never seen a flexible connector to a hydronic expansion tank.

  • kcopp
    kcopp Member Posts: 4,667

    In some cases it makes sense to get it out of the way. Actually many of the tank brackets allow for this. Axiom, Calefactio, etc.

    I use barrier pex and a couple adapters.

    HydronicMike
  • hot_rod
    hot_rod Member Posts: 27,372

    I have seen thermal expansion tanks on water heaters connected with flex tubes. Most are 3/4" however.

    \

    Screenshot 2026-03-10 at 7.39.01 PM.png

    If a faucet braided connector is rated for the temperature and pressure it should be fine. Most likely it

    is an EPDM hose with stainless braid.

    Capacity could be a concern on larger boilers, perhaps. Amtrol probably has a sizing formula for the tank connector tube :)

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    HydronicMike
  • 4GenPlumber
    4GenPlumber Member Posts: 132

    Where are you guys working? I have never seen a flex connector to any expansion...ever. And I have seen some really poor installations before. Home Depot subs that use flexes on water heater hot and cold wouldnt even put a flex on around me. Maybe in seismically active locations? Technically, even where i am in NJ is a "seismic area" but not really.

  • kcopp
    kcopp Member Posts: 4,667

    I have not seen flex connectors but can imagine someone out there would do it if they dont have tool / skill/ time…

  • mattmia2
    mattmia2 Member Posts: 16,562

    unless it is a huge commercial system the flow from expansion is far less that the max capacity of 3/8" soft copper.

    if i really wanted something flexible i'd use soft copper.

  • hot_rod
    hot_rod Member Posts: 27,372

    Actually a lot of the Euro boilers that have pancake type expansion tanks inside the cabinet have small flex lines connecting them. I had an early Laars Mascot (Baxi 330) that had a SS flex expansion line. Straight connections with fiber washer connections.

    Screenshot 2026-03-11 at 9.40.00 AM.png

    Zilmet has tank/ flex kits for systems that are common in other places around the world.

    Screenshot 2026-03-11 at 9.42.30 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • HydronicMike
    HydronicMike Member Posts: 336

    Yes but are they have oxygen barrier for hydronic systems?

  • hot_rod
    hot_rod Member Posts: 27,372

    You would need to ask the manufacturer what the inner tube is made of. This example shows a PVC inner liner. That is not considered O2 barrier material. PVC is not typically rated to 180° either.

    Screenshot 2026-03-11 at 11.21.28 AM.png

    I don't know the SS braid is tight enough to be O2 impervious? Stainless is, but maybe not the braid.

    I don't know that 24" of non barrier tube in a system would create a O2 ingress problem?

    Pump gaskets and other components are not O2 barrier material in hydronic systems. A 100% O2 ingress free system is near impossible.

    The amount of O2 ingress is directly related to fluid temperature, so systems at 180 are more prone to O2 ingress than systems running 120°

    What temperature would the flex be exposed to under continuous operation?

    You can always add a hydronic conditioner, like Fernox, etc, which have a component to address small O2 ingress. Oxygen scavengers.

    I have seen flex connectors used on panel radiators, and unit heaters also, must be someone builds hydronic rated flexs like Zilmet and other Euro expansion vessel manufacturers, sell?

    A short piece of Watts Radiant Onix hose would be an option.

    Caleffi solar expansion tank kits included a stainless corrugated flex connector, 3/4"X 18"

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 16,562

    i'd imagine the stub to the expansion tank is relatively cool.

  • HydronicMike
    HydronicMike Member Posts: 336
    edited 6:25PM
  • mattmia2
    mattmia2 Member Posts: 16,562

    even then there will be little flow other than briefly

  • hot_rod
    hot_rod Member Posts: 27,372

    every time the boiler heats, water expands, there is water movement into the tank

    That fluid movement will be the temperature the boiler operates at. In theory it happens at every heat up cycle.

    On high temperatures evac tube as solar arrays a cool down tank was installed in front of the solar thermal expansion tank as there are no expansion tanks , even solar versions, that could handle 300 plus temperature on a regular basis

    Amtrol suggests a Heating leg if tanks could be exposed to over 240F.

    IMG_2079.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 16,562

    unless it is a very large boiler the system water will get up to setpoint over maybe 10 minutes or so and the expansion is a couple gallons so you have the pipe and the tank getting something like < .25 gpm. the surface of the tank and the pipe will radiate a fair bit of that energy at the rate is is being added as the temp increases beyond ambient and the transfer rate increases.

    a small fin tube system that contains maybe 20-30 gallons will have maybe half a gallon of expansion volume that happens over 5 minutes or so.

    a gravity conversion system will have hundreds of gallons of water with maybe 2-5 gallons of expansion but the whole system will heat over maybe half an hour to 45 minutes.

    in a residential or small commercial system the flow rate to the tank is tiny.

    you could get more heating of the tank if you get gravity circulation in the line to the tank.