Mail4tommo
Mail4tommo Member Posts: 51

Lets say i open up a chimney that has 12x12 tile, and there was a 6" hole for the old boiler for example. How would I make that 6" hole lets say 8-10"? If need be? This is hypothetical. I'm curious for down the road if it comes up.

I'm not worried about free space or proper venting of X amount of btus through the chimney at the moment, I'd figure that out if the time come.

Just want to know the process.

Thanks in advance

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,277

    Flue tile is actually remarkably fragile — but can be cut with diamond saws.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Bob Harper
    Bob Harper Member Posts: 1,154

    Since you must seal a clay thimble flush to the inner face of the flue tile, However, since the flue must be suitable for the class of service, just bust out whatever since hole you need, install a stainless steel liner with a ss thimble then cement in around the thimble. Done.

    HydronicMike
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,103
    edited March 9

    Hammer and chisel.

    Try to drill it it will break anyhow.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,084

    Simple job — just drop a gremlin down the chimney and have him cut the thimble opening from the inside out. When he gets to the basement, hand him the masonry tools through the hole and have him seal the crock to the liner before he comes back up. Don’t forget to tie a rope to the gremlin so you can pull him back out. 😄

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • delcrossv
    delcrossv Member Posts: 2,203
    edited March 9

    Drill a series of 1/4" holes about 3/4" apart outlining your desired opening with a carbide bit and then chisel between the holes. No gremlins required. 😉

    You will need to reach in and mud around your new thimble on the inside.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,084

    OR you can do what I used to do. Tell the customer that they need a chimney man to install the new 8" crock and to look in the Yellow Pages for a good chimney professional in the area. (Do they still print the YellowPages?). Then call you when the chimney is ready for the new heater.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 16,545

    is or was sheetmetal allowed for the thimble? in the installations where there actually was a thimble it was always steel, not clay.

    delcrossv
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,084

    I only remember getting called on "sealing the thimble to the tile liner" one time on my entire career of oil and gas heat installs. I needed to shorten the first piece of galvanized pipe to about 8" so I could mix up cement and use my hand to lay that mud around the opening of the tile to the sheet metal. The inspector removed the vent pipe and used a mirror to inspect it. Go Figure!

    After that day I tried to make that connection with some type of masonry product. It added about 20 more minutes to the job, unless you forgot it. the it adds 2 more hours with fast drying cement products. After setting the 8" thimble you need to wait for the cement to set up before you can connect the rest of the vent connector. I found a product called Struct-O-lite that sets up within 30 minutes, and started using that on all the removable vent connectors during maintenance calls.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 16,545

    structo is premixed base coat plaster. strocto lite is a lightweight version of premixed basecoat plaster. presumably the lightweight version replaces the sand with vermiculite just like if you mix it with separate plaster of paris, lime, and sand/vermiculite.

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,084
    edited March 9

    @mattmia2
    That is the information I got from a well-known chimney service company in Philadelphia over 40 years ago. I have used that product ever since. I would label it “Chimney Cement” on the 5-gallon bucket I carried on my service truck. None of my chimney connectors ever started to dry out or crack away in the 40+ years I have used that stuff, and not one time did any of those plaster jobs catch fire. I don't believe there is anything in that product that is combustible or flammable. I could be wrong.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 16,545

    Was anything i listed flammable? It probably dehydrates at a bit of a lower temp than portland cement but if your stack is getting anywhere near that temp you have bigger problems. I'm sure you worked on lots of systems where the chimney was unlined and built with lime mortar.

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,084

    Not “lots of systems,” but I have come across a few in my time. I remember one that was having a problem with a downdraft causing the pilot flame to blow out in the water heater. I told the customer to call a chimney service of their choice to have a liner installed.

    It was a two-story Colonial with a 12/12 pitch roof, making the chimney top about 40 feet above the ground level where my ladder would be set. There was no clay liner, because they didn’t use them in the late 1700s. All the mortar was cracking away, and the residents were over 80 years old and had a hard time getting to the water heater to light the pilot—especially in the snow, since the boiler and water heater were accessed from an outside doorway on the other side of the rear kitchen entrance.

    The chimney man they called was a knucklehead who was not even insured. He took a mirror and looked up the unlined flue and said, “No problem here—I can see clear to the top.” Then the son called me and said the chimney was fine.I needed to explain that the chimney didn’t need cleaning; it needed pointing or a liner. The guy they called only cleans chimneys and really does not know much more about chimneys than that.

    The bottom line was that I ended up selling them a Pilot relight kit so that when the pilot blew out there was a good chance it would relight by itself. If the pilot didn’t relight soon enough, then the gas valve would lock out and the spark would continue until someone pressed the pilot button down. The spark would then light the pilot again without needing to open the burner door. After about 60 seconds the pilot button could be released and the water heater would work properly—until the next Nor’easter blew it out again.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Bob Harper
    Bob Harper Member Posts: 1,154

    You make the 'crock' or 'thimble, traditionally using a round terra cotta flue tile section or a purpose made one cemented flush to the inner wall of the flue. The actual vent connector of steel is then inserted into this crock and it, too must be sealed circumferentially with a refractory mortar.

    When patching or replacing connectors you want something refractory to meet the code and that can take the heat but is lightweight with a very low compressive strength so it can easily be removed. Ordinary Portland Cement (OPC)-based mortars are typically stronger than needed. Also, an OPC-rich mortar will shrink and crack badly. The best product in a bucket is "Chamber Tech 2000" or one of its clones. This is a very sticky refractory parging mortar that contains fiber reinforcement already mixed in. Even if you do get cracks, it is knitted together. You can also use it much thicker than OPC-based mortars. Regardless of the mortar, wet down the mating surfaces with a mixture of tap water and dish soap as a wetting agent so it soaks in.

    In situations where you need a flash set, such as to hold something in place while you work on the other end, such as vent connector, you can add a little stucco mix to the CT2K and it will set in 5 minutes on a hot summer day. I credit chimney sweep Phil Taggart at Chimney Cricket outside Philly with calling it his "Zip Mix".

    Note that drywall compound begins to calcine around 150C/ 302F. Lime mortars begin to break down around 500F and OPCs around 600F. If you get water into the mortars, acids from flue gas condensate will combine with the alkaline mortars to form soluble salts, then displace to surfaces where they concentrate as efflorescence, which can then be washed away. You're left with sand and salt between the masonry elements as it is no longer mortar. That's why NPFA 211 has been calling for a non-water soluble calcium aluminate refractory cement mixture btw flue tiles for over 25yrs. It comes in a powder, such as Heat Stop 211. HTH.