Flow control valves
Mail4tommo
Mail4tommo Member Posts: 69
Can you use spring check valves in place of a "standard" b & g flo control? Also is there any other options besides the B & G's?
Thank you in advance
    mattmia2 Member Posts: 16,739
    usually unless the circulator is marginal, the weighted check has a bit less resistance than the spring check. the nice thing about most of the wighted check designs is they can be manually opened to purge and bleed the system.
    taco, b&g, watts, and caleffi make flow check valves(caleffi look like they are only spring flow checks)
    https://www.supplyhouse.com/Flow-Control-Valves-275000
    you can put a flow check in the flange of most newer circulators too
    Mail4tommo
    hot_rod Member Posts: 27,445
    Caleffi had a spring check with a manual lever, operated with a knob. It was sold as a B&G product also.You can still find them around. Low Energy in Colorado shows them, also e-bay
    The spring checks Caleffi sell now do not have the manual lever, same spring, .25 psi, 1-1/2 and larger is .50 psi.
    The B&G iron FloChecks were .33 psi pop. I think they have been discontinued
    mattmia2Mail4tommo
    i have a b&g branded version of that, i did not know it was made by caleffi
    Mail4tommo
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    Just to note , most control valves can be cleaned and put back in service .
    mattmia2Mail4tommo
  • Mail4tommo
    @hot_rod so then my 2nd question is. If the circulator on the supply has a ifc installed, in some cases the weighted flow control would still have to go on the return on the secondary? For example , 2 zones upper and lower both Hi temp baseboard. The weighted check would go on the return on 1st or 2nd floor zone? sorry for my dyslexia, you are a life saver,
    in some, fairly rare cases you need checks on both supply and return
    The check in the pump and another hydronic spring check on the return
    That will be the best protection and also lowest pressure drop
    Most prone are high temperature system where the buoyancy difference dtives ghost flow. Tall buildings with straight vertical runs, and of course mis- piped systems