Ultra 230-4 outdoor sensor
heaterbeater
heaterbeater Member Posts: 2
Is the outdoor temp sensor the same resistance profile as two indoor ones? The book is unclear . Thanks.
    109A_5 Member Posts: 4,047
    edited March 5
    Troubleshooting section. All the same resistance chart. Probably a 12K at 77F (25C) degree Thermistor.
    Big Ed_4
    hot_rod Member Posts: 27,473
    I’m pretty sure they are. Take an indoor one. And connect it to the outdoor sensor connection and see what it reads.
    There would be a chart for the outdoor sensor if it was a different resistance profile.
    Tech support at Weil should know for sure.
  • heaterbeater
    Thanks .I hope you're right.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    Instal the sensor and check the readings .. Instal the outdoor sensor NW corner not over a window or heat source ..