Add a mixing valve ?
This is from another thread on a system with zone valves. I figured I would start a new one with this new question and hopefully get more views… (Hope this is ok)
Previously looked at a job with 3 zones total. One of which is an in-floor concrete slab zone with no mixing valve or anything to control water temperature. It is getting 180 degree water just like the rest of the system. Customer complaint is that the zone is always too hot.
So now I've gotta schedule a time to go back to the house and determine how to control temperature to the in-floor radiant zone. The current system has a single circulator and 3 honeywell zone valves all on the supply side. (pic attached)
What is the best way to control water temperature to the in-floor radiant zone? Is there a way to do it without adding another circulator? Can I install a manual 3-way valve for this?
A manual mixer is better than what's there, but will still have variations in SWT so it's not the ideal option. Adding a circulator is the only way to really dial it in for maximum performance
There is already a thermostat and zone valve in place for the in-floor zone.
Naturally the customer wants something as easy and cheap as possible without re-piping the whole system. He is upset with the original installing contractor who did this 2 years ago, (which is why I got a call ) . He spent a lot of money to install brand new boiler system with new zone that is not correct. So I understand his frustration.
So I'm looking for an easy alternative for this situation to help out this guy. He is 83 years old and understands it's piped wrong. He just wants an easy solution
I think on cold days with a manual mix valve there is a good chance the system will still end up over temping that zone quite a bit. I would just cut to the chase and get a thermostatic valve and a circ. If you want to help the guy out cut him a deal on labor. just my opinion
https://www.supplyhouse.com/Honeywell-Home-T100R1012-Valve-Actuator-with-Remote-Sensor-86-158F
https://www.supplyhouse.com/Grundfos-519601-3-4-Iron-Pump-Flange-pair-9574000-p
I would either do it properly, or leave it like it is.
A 3 way thermostatic would be the least expensive way to get accurate control. But it would involve some repiping.
Any mixing valve will need a dedicated circulator, it needs to pull hot and cold together to mix properly, so a pump on the discharge M mix port.
Here are a couple of the simplest options.
Since you have zone valves this first option is workable. No need for that pressure bypass unles you have more that 4 zone valves.
So basically add another zone valve, make a loop from zone valve to return. A valve in that loop to balance just enough gpm for the radiant. In that loop, two close tees for the mix valve and its pump.
This give you independant control over just the radiant woithout running any other zones.
Living the hydronic dream1 -
I understand. Doing it properly is best option for it to work correctly.
Just a thought in my head… What about a limit switch or something secured to the supply line to the in-floor zone, wired in series thru the thermostat signal to the zone valve? Or actually maybe better on the return line coming back ?
Could set it at around 100 degrees on the return line to shut off that zone, and then the warm water in the tubing would just sit there as the concrete absorbs heat. Then once it cools off, the zone valve opens to flow more water… I know it's not the most ideal solution, but would it help this problem ?
That valve would be pulsing on/ off every several seconds as the cooler water comes back.
I wish it were that simple
Living the hydronic dream0
