Furnace fires up for a while then quits
bigchungus
bigchungus Member Posts: 3
I've got a riello 40 f3 burner. All of a sudden it will only run for a few hrs at a time, then I have to flip the breaker off for several hrs before it'll fire again. I've already changed out the fuel filter and control box and was going to go to the nozzle next. Could there be something I'm missing? Any help is appreciated as it has been between -30 and -40 where I'm at!
  • Big Ed_4
    Big Ed_4 Member Posts: 3,515
    edited March 3
    If you have to retart the burner by pushing the reset button on the burner , the burner experienced a flame out. If you have to restart the burner by shutting off the power , I would suspect a electrical problem .. While it is down test with a electrical meter, where along the line the power is dropping out ..
    HVACNUTMaxMercy
    HVACNUT Member Posts: 7,409
    Is the breaker tripping, or you just turn it off and on?
    Is the boiler hot but not heating the space? Is there power to the circulator(s)?
    If the boiler is cold is there power at B1 in the aquastat?
    Why the nozzle next? Why not the fuel pump, or motor, or the draft regulator? Why not the oil tank itself?
    mattmia2MaxMercy
  • Grallert
    Grallert Member Posts: 1,105
    Heating systems can be confusing sometimes. Are you opening and closing the breaker at the wall panel? Is that what's tripping? Or is the red button on the burner tripping and you have to press it to start the burner. Lets start there.
  • bigchungus
    After a few hrs of running properly the furnace will quit producing heat but will still try to start up. When that happens I flip the breaker off at the breaker box. Wait several hrs then turn it back on and usually the furnace will fire back up
  • bigchungus
    Hvacnut I haven't checked all that stuff because I don't know how to. Just a regular home owner. Not a pro.
    HVACNUT
  • Grallert
    Ok there is a list of things that could be the issue. Can you read the pressure on the boiler gauge? You know what? Some pictures of the boiler would help. Get the whole thing in the frame if possible. By turning it off your letting it cool, that could be a clue. Does it trip the breaker? I'm curious about water pressure in the system.
  • MaxMercy
    MaxMercy Member Posts: 597
    "After a few hrs of running properly the furnace will quit producing heat but will still try to start up."
    Can you define "try"? Is it making odd noises during the start attempt, is it cycling?
  • Big Ed_4
    You will need to call in a local tech to find the problem. It could be too much of a electrical load or bad breaker ..If you need to cool it down first to reset the breaker.
  • HydronicMike
    HydronicMike Member Posts: 323
    I think it’s a component and/or set up problem.
    Turning the breaker on and off may have nothing to do with an electrical problem.