Standby DHW Tank Question
SInce installing our indirect dhw tank with the new boiler I have a question. We kept the electric dhw tank and isolated it to be used as a backup. Last night I started wondering about the water in the tank. Should it be drained and refilled every so often?
Thanks!
Comments
-
Funny how things show up in the middle of the night…
The answer to your question is n— yes it should. While stagnant water is usually OK, it can decide to grow nasties…
How often? Well… At the very least weekly, I'd say. And if it's that rarely, I'd run it right up to 140 F and hold it there for an hour every time it is refilled, then turn it off. But I'm sort of conc=servative.
An alternative would be to pipe it so that the feed to the regular domestic hot water went through it first, but without heating it. That will keep the water in it fresh at all times, and is probably what I would arrange.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
You could valve and series the tanks, so fresh water always flows through the electric tank first. If the indirect is down you could valve it off, flick on the electric tank breaker.
This also give you a small amount of pre-heat the first tank being at ambient room temperature.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 117 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements