boiler filling normal vs really cold winter temps

Options
bbillcee
bbillcee Member Posts: 67

Hi guys

i've had the automatic water filler on my boiler off for 2 seasons now to see how it fills, in regular winter temps (30-40's) i fill it about once a month, i dont wait for it to trip out the low water but once i see the red flashing light start to come on i fill. in the really cold temps its about 2 weeks maybe slightly more. I watch a guy on youtube who is always saying if u add fresh water to often in cuts a hole in the boiler….is two weeks ok?

Comments

  • tcassano87
    tcassano87 Member Posts: 118

    The guy on YouTube is probably referring to water being added too often because of leaks, faulty air valves and things causing water to be introduced when it shouldn't be. With how cold it's been your certainly going to refill more often than you would with typical temperatures. If your boiler is working properly, no leaks in the system and it's simply getting water added because of extra usage then you're fine

    bbillcee
  • Captain Who
    Captain Who Member Posts: 640

    It seems like it may be normal, rather than excessive. Hopefully you are filling from the hot water tank because that has lost some of the air that is in cold tap water. Are you treating your water with anything? Do you know your tap water hardness and chlorides (water company usually reports on stuff like that if you can find it online). Are you keeping your pH in the 9 to 10.5 range?

  • ethicalpaul
    ethicalpaul Member Posts: 8,513
    edited January 25

    That sounds like possibly too much water. You don’t say how much but it sounds like a couple inches every two weeks.

    I’d try to get it 1” per month. Look for steam leaks especially if you set back your thermostat

    PS: why let it get low enough to flash lights? I’d refill it whenever it was 1” low

    Then log each addition of 1”. You might be using more than you think

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • PhilKulkarni
    PhilKulkarni Member Posts: 111

    This past November and December, I added 2.75 gallons of distilled water altogether to the boiler of my one pipe system. However, since this past Thursday until yesterday, due to the cold spell we are having in the NYC area, my boiler has been working overtime( 12+ hrs yesterday) and I have already added 2 quarts in 3 days. Two of my MOM vents are spitting water for a few mins before the boiler shuts off adding to the water loss. Two others are working fine. Fortunately, I have several Ventrites that close properly and while I can substitute one of the spitting vents with a Ventrite, the #C on my largest rad would be a problem. I have tried a Gorton #C and it does not close at all due to the wet steam. I could buy a new MOM #C but before going that route I would appreciate any suggestions?

    My main vents which are BMs close normally.

    How reliable are the manufacturer’s guidelines for limits for adding fresh water each year? At the current rate, I will exceed them handily.

  • ethicalpaul
    ethicalpaul Member Posts: 8,513

    You have a serious leak(s) if you are adding 2 quarts in 3 days, no matter how cold it is out.

    it does not close at all due to the wet steam

    Just for my education about people's thinking, can you tell me exactly what you mean by "wet steam" here?

    Does your water level drop in the gauge glass significantly during boiler firing?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    mattmia2
  • Captain Who
    Captain Who Member Posts: 640
    edited January 25

    @PhilKulkarni You could try a Heat Timer Varivalve. They adjust from 0.20 to 1.13 cfm at 3 oz. pressure. Your MOM C is 0.583 cfm. Varivalve at 50% closure setting is actually 0.766 cfm.

    My boiler is running about a 28% duty cycle now with t-stat at 64 F in Union County, NJ at about 10 deg F outside and avg. windspeed of 2.1mph and gusts of 8mph.. What duty cycle is yours doing?

    STEAM DOCTOR
  • PhilKulkarni
    PhilKulkarni Member Posts: 111

    @ethicalpaul, my mains and returns are above ground and have been checked for leaks by me as well as by other plumbers. The risers are in the walls but none of the walls show any evidence of leaks unless the water is evaporating on its way down. All the visible pipes have fiberglass insulation while the risers have the original asbestos. None of the radiator valves leak. Only the vents, and only 2 at the moment, are spitting water. So, short of pressurizing the system or using thermal imaging I have no way of telling if the system leaks or not. Resorting to these measures here in Westchester is next to impossible as there are no HVAC companies here that can do these diagnostics. The BMs did leak steam, but since changing to silicone O rings they have been working perfectly for the past 4 years.

    When it comes to the type of rad vents, both the Hoffman and Ventrite float types have been good at closing shut. In the bimetallic types, the MOMs are the next best but the Gortons haven’t worked at all for me. My steam carries a high percentage of suspended water in it and when this wet steam hits the float type vents they still move up and close the orifice perfectly while the bimetallic types don’t in all cases. Every design in each category is a bit different though the operating principle in each category is the same. Then there is the issue of manufacturing QC that I will not delve into.

    Per your definition, I have a significant carryover. At a pressure of 0.6PSI my water level drops 4.5” from the boiler mark. For the past three days, the boiler pressure has inched up to 0.8 and the boiler occasionally cycles once on pressure even though it runs for 25-30 mins 2 times per hr. instead of once every 1.5hrs at higher ambients than at present.

    @Captain Who, I have tried the Varivalves in the past; they work very well until they don’t because they succumb to rust particles. I was taking them out and cleaning them every month, perhaps more often. I am inclined to try them again since I believe more rust is being inhibited by the 8-Way. I might be able to stop the two spitting rad vents by operating the boiler with the water level 1-1.5” below the water mark while I get the Varivalves tomorrow from Amazon. Since my boiler has logged over 12 hrs yesterday and 10 hrs the day before, I’d say the duty cycle is north of 45%.

    Thanks to you both for your insights.

  • Captain Who
    Captain Who Member Posts: 640
    edited January 25

    I should've mentioned that varivalves will spit water, but if you have used them I guess you know that.

    I forget if you have mentioned the height of the top of your close nipple on the hartford or not. I'd be careful of running the boiler at lower than NWL, depending upon where your close nipple is located vertically. In "my experience" it is NOT GOOD for me when the water level goes below the close nipple. I actually run mine close to 1in. above before steaming starts to protect myself from that situation. As the particulates increase between draining and flushing the sight glass starts to surge more. Right now it is less than 1/4 in. of motion.

    Sorry if you have already done or mentioned. Pitch for mains and dry returns should be 1in. per 20 ft. and for radiator supplies twice that pitch.

  • Big Ed_4
    Big Ed_4 Member Posts: 3,444
    edited January 25

    I would say your doing good , you seem to be on top of things .. Its hard to find those small leaks , and the larger the system gets….

    There was an error rendering this rich post.

    ethicalpaul
  • PhilKulkarni
    PhilKulkarni Member Posts: 111

    This is a quick update: I replaced one of the spitting MOM#5 with an adjustable Ventrite fully open and the spitting stopped. I replaced the MOM #C with a Varivent and this vents gurgles for about a min before shutting off- a lot better than spitting. The downside with the Varivent is that it is the first vent to break the vacuum and the rad is in the living room.

    Too soon to determine if water usage has declined with the new vents.

  • ethicalpaul
    ethicalpaul Member Posts: 8,513

    thanks for the report. Yes by my definition you have significant carryover (not suspended water in your steam) and you should address that. Your vents will all work better.

    Have you ruled out a boiler rust hole by flooding it and looking for water running out under the boiler?

    Your usage seems high still, but maybe it’s just spillage from the various vents which can add up fast.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Captain Who
    Captain Who Member Posts: 640
    edited January 30

    @PhilKulkarni I have been using the Varivalves for 20 years an mostly I am happy with them. I just found one that was letting a small amount of steam towards the end of the burner cycle; not enough to audibly hiss but the old inspection mirror revealed it. Replaced it with a new one that tested a year ago when I bought it at 153 deg opening temp. I try to have on hand a couple for spares every heating season and test new ones I buy in a pot of water with a vinyl hose and hose clamp and a digital thermometer. I have found that the temperature at which they open can vary by a whole lot. Of these two I bought last year one was 130 F and the other was 153 F. I have seen them as high as 180 F, but not recently. My thinking on them is that if you don't want the particular radiator to break vacuum as soon after the burner cycle, put a lower temperature one in.

  • mattmia2
    mattmia2 Member Posts: 16,164

    under some circumstances the velocity of the steam can be enough to pick up the condensate and make vents spit too, sometimes slowing down the vent can help regardless of if it is just some water sitting somewhere or a lot of carryover

    Captain Who
  • mattmia2
    mattmia2 Member Posts: 16,164

    you could put a vacuum breaker somewhere if the vent noise is a problem

  • patrykrebisz
    patrykrebisz Member Posts: 92

    Varivalves fail "upwards". That means they still kinda work even when internals plungers has disconnected from the bellows.

    I've made a video about it (if you care):

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

    Captain Who
  • Captain Who
    Captain Who Member Posts: 640
    edited January 31

    Of the 8 varivalves that I have removed over the years, 3 are blocked, 2 are rattling, and the other 3 have some other fault, like leaking a bit of steam. To be honest there are probably a couple I didn't keep and threw away.

  • patrykrebisz
    patrykrebisz Member Posts: 92

    yeah, those are weird valves. that said, at least one of my radiators i'm keeping the "broken" valve on it because it "works" so well.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

  • ethicalpaul
    ethicalpaul Member Posts: 8,513
    edited January 31

    Not despite my many attempts to make such a thing occur, it hasn't. But I would love to see it!

    And how could any vent allow steam to travel more than the steam itself condensing does?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    reggi
  • PhilKulkarni
    PhilKulkarni Member Posts: 111

    Paul, I have not checked for boiler leaks since my boiler is relatively new( in its 4th season) and the water consumption is similar to the 2022-23 season when we had a long cold spell. I agree with you that without leaks the water consumption should be zero regardless of the ambient. But with lower temperatures, the boiler runs more frequently and longer, magnifying even small leaks in the the boiler, pipes, valves and vents which might not be very apparent.

    I’m still trying to crack the code on how to reduce carryover and slow the boiler rusting process—basically attempting to keep a juvenile metal beast from eating itself. It’s turning into a full‑blown Sisyphean hobby, especially since half the homeowners on HH seem to be running secret research labs devoted to this very problem.

    Meanwhile, I watch videos of your system operating at near-mythical perfection—no carryover, no rust flakes the size of meteorites, and only a dainty cup of makeup water per season—and I am filled with equal parts admiration and existential envy. Admiration because your setup is clearly a one pipe unicorn, and envy because the rest of us mere mortals are stuck babysitting boilers with “quirks” that would drive a shrink to drink.

    So many things go wrong that we basically have to live in a permanent state of cheerful self-delusion, treating every weird gurgle, bang, hiss, and outright tantrum as if it’s a solvable engineering puzzle, instead of what it really is: our systems developing new warts just to drive us nuts.

    Captain Who, using steam systems requires one to embrace stoicism. I have learned not to fight with them but to live with their failings as long they produce heat. Doing anything else will compel you to pursue some of life’s finer things like plotting Ventrite graphs of opening temps and pressures which predictably takes a 20 yr chunk out of your life.

    I have had good experience with the green colored Ventrites of yesteryear, the one I got now is blue, notwithstanding this technological breakthrough, I never believed that changing the vents would be the end of this saga.

    But I live with it, enjoy the shared misery and carry on.

    ethicalpauldabrakeman
  • Captain Who
    Captain Who Member Posts: 640

    Ha ha true Phil. I do incoming inspection on my newly purchased Varivalves because I want to weed out any bad ones so I can return for a replacement, before I have to use them in my system, which I don't know when that will be. Then there is the issue of ones that open at too high of a temperature breaking vacuum sooner than I would like. Maybe the company has stopped allowing that. Dunno. Also I'm a nerd but that is besides the point……I think…😀 When they go into the system they also are fairly out of sight being that all my radiators have perforated metal covers over them and you know about out of sight out of mind. I would like to try one of those adustable Ventrites. Maybe I'll order one with my next order of Varivalves.

  • ethicalpaul
    ethicalpaul Member Posts: 8,513

    not zero, in fact I just added a gallon yesterday. This cold snap is making every boiler use more water.

    I probably use more than a lot of folks because my low pressure switch/timer relay setup means even more interruptions in calls for heat than if I let it get up to 2psi like my pressuretrol wants to do.

    Each of those interruptions is a loss of all the humid air in my system and an “inhale” of dry air from my house.

    But I only add freshly boiled distilled water so it doesn’t bother me.

    I’m glad your boiler is intact! Your Big Mouth vents might be losing a decent amount of steam when closing, I know mine did when I had one

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,560
    edited February 1

    Lots of bad experiences with vari vents. Early failures and excessive venting. Find that they throw systems out of whack and out of balance. And they tend to spit

    ethicalpaul