Can a leaking site glass cause an overfill?
We have a 1950ish single pipe steam gas boiler. A couple months ago we had a flooding issue as well as a leaking site glass (like drips and steam escaping when its full of steam) and I've been running the boiler with the water off and manually monitoring and filling since it flooded. Ive called our service guy and hes not returning my calls, hoping hes just crazy busy. I was tired of waiting so I replaced the site glass gaskets and nuts and no more leaking. We've been running the boiler for a week with constant monitoring with the water open and relying on the autofill and so far (knocking on wood) it has not flooded. Is it possible the leaking site glass was the issue or do we likely still have an issue with the float needing cleaned? Thank you as always!!
Comments
-
The sight glass itself is entirely passive — it doesn't do anything except tell you where the water is. So no, it can't cause an overfill.
In your setup, the most likely causes are the float, assuming you have a float type low water cutoff, sticking down keeping the autofill on or the autofill itself leaking.
Whatever, the float LWCO should be blown down once a week anyway…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
With the gaskets on the sight glass leaking it may not always show the true water level in the boiler.
0 -
Supply valves can fail to shutoff completely and the boiler could inadvertently get overfilled.
0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements