Burnam oil burner not heating both zones
I have a 35+ year old Burnam boiler that had been working well. It is not heating one of the zones. Temperatures are freezing cold with blizzard on the way. I am hoping to troubleshoot. It is set to automatic. Oil tank full. The filter is relatively new. Thermostat is 1 year old and basic. It may be zone valve. I just switched to open and heat pipe heated up. Any suggestions?
Comments
-
Is this hot water or steam?
How many thermostats do you have? Usually there is one per zone.What exactly is set to "automatic"? A switch on the thermostat?
—
Bburd0 -
-
-
bburd- Good news. The heat is on now in both zones. Thanks.
0 -
Most likely the zone valve power head has failed, or it could be a problem in the thermostat circuit or zone valve end switch circuit. You can check these things with a multimeter if you are handy with electricity. If not, it might be best to call for service.
For now, since the weather is very cold, I suggest you leave the zone valve manually opened. That zone will heat at the same time as the other zone, so you should be protected from frozen pipes.
—
Bburd0 -