NHB 150 making DHW at 165 supply temp?
DIYorBust
DIYorBust Member Posts: 84
After replacing the PCB board in this navien NHB 150, I noticed that when making DHW it is down modulating to keep the supply water temp going to the indirect water heater at around 165. I feel like it should be supplying 180, to maximize the DHW water supply and recovering time. Are we missing something with the settings or jumpers? Thanks!
    HVACNUT Member Posts: 7,305
    How do we know if you missed something if we don’t know what you didn't miss? I'll blindly throw a dart anyway.
  • DIYorBust
    Thanks, I figured it out, dip switch 8 on the PCB for exhaust temp limit was in the wrong position. This boiler has a polypropylene vent and it is safe to operate at 180, but the boiler was limiting the vent temp for PVC.
    hot_rod Member Posts: 27,056
    Generating DHW with the lowest boiler supply temperature increases efficiency of the boiler.
    So if 160 boiler temperature was providing adequate DHW, why boost it to 180?
    A lot of recovery time has to do with boiler capacity, piping and pump sizing and the size of the coil in the indirect.
    GGrossbjohnhy
  • DIYorBust
    160 does not supply enough hot water.