Replacement for Barber Colman actuator needed
does anyone know if there is a company that sells refurbished or replacement for Barber Colman actuators? I have a model
MS-83010, that is approximately 40 years old. I would like to find just the actuator and not have to replace the three way valve it is connected to, or the room thermostat that controls it. Thanks to all
Consulting1 -
Belimo , Siemens, etc make retrofit kits for lots of different valves. You can get kits that either use open air accuators or hydraulic valve tops. We did this all the time when I worked at Siemens. The big thing you need to make sure that you have an enough VA on your 24 volt circuit. The 0-10VDC or 4-20mA control signal might need to be scaled to the controller output. Typically we used functional devices PSH500A transformers to provide 24 volt power to devices and used a 14/2 cable as the power trunk to minimize voltage drop over distances.
If you look at a Belimo or Siemens catalog they will have a bunch of items to help you.
Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.