Boiler system valves DZR rating

Options
Blend9684
Blend9684 Member Posts: 18

Seems I ordered ball valves with a low DZR rating from SupplyHouse - "Please Note: This product is susceptible to dezincification and does not hold a high DZR rating. This product should not be used in applications where brass parts may be exposed to hard water (high sulfur or mineral content)."

I was planning on filling the boiler from my well water after the sediment filter but before the softener.

Hardness was 68.4 PPM (moderately hard) when I last tested in 2014. Do I need different valves for hydronic components? I wasn't sure if closed-loop mattered.

Comments

  • hot_rod
    hot_rod Member Posts: 27,058

    Valves used on the potable water side need to be LL low lead.

    Lead or or low DZR brass should be fine on hydronics as it is not seeing a constant renewal of water.

    What boiler do you have?

    I would check the boiler water quality spec. It should be in the boilers manual. Hard water is generally frowned upon. 68 ppm is under 4 gpg

    7- 10 gpg seems to stick in my mind from manufacturers, 171 ppm.

    Screenshot 2026-01-11 at 4.27.07 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGross
  • Blend9684
    Blend9684 Member Posts: 18
    edited January 12

    Bradford White FTCF199N per the book (they add additional letters/numbers when ordering). Same as the Laars FTCF199N. Floor-standing combi.

    I'm not seeing anything in the books regarding water quality. DHW would use softened water but I didn't think ion-exchanged water was good for the boiler side.

    Total system volume is only ~42 gallons with 21-gallon buffer tank. Probably straightforward to source elsewhere and just use the well water for makeup and not initial fill (though water might not be that hard).

  • hot_rod
    hot_rod Member Posts: 27,058

    odd that the manual talks about glycol but not plain fill water?

    I agree with this statement in the manual however, I’m a big proponent of hydronic conditioners. Your water seems fine, just squirt a can of Rhomar, Axiom or Fernox in

    IMG_1368.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream