Seems I ordered ball valves with a low DZR rating from SupplyHouse - "Please Note: This product is susceptible to dezincification and does not hold a high DZR rating. This product should not be used in applications where brass parts may be exposed to hard water (high sulfur or mineral content)."
I was planning on filling the boiler from my well water after the sediment filter but before the softener.
Hardness was 68.4 PPM (moderately hard) when I last tested in 2014. Do I need different valves for hydronic components? I wasn't sure if closed-loop mattered.
Comments
-
Valves used on the potable water side need to be LL low lead.
Lead or or low DZR brass should be fine on hydronics as it is not seeing a constant renewal of water.
What boiler do you have?
I would check the boiler water quality spec. It should be in the boilers manual. Hard water is generally frowned upon. 68 ppm is under 4 gpg
7- 10 gpg seems to stick in my mind from manufacturers, 171 ppm.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Bradford White FTCF199N per the book (they add additional letters/numbers when ordering). Same as the Laars FTCF199N. Floor-standing combi.
I'm not seeing anything in the books regarding water quality. DHW would use softened water but I didn't think ion-exchanged water was good for the boiler side.
Total system volume is only ~42 gallons with 21-gallon buffer tank. Probably straightforward to source elsewhere and just use the well water for makeup and not initial fill (though water might not be that hard).
0 -
odd that the manual talks about glycol but not plain fill water?
I agree with this statement in the manual however, I’m a big proponent of hydronic conditioners. Your water seems fine, just squirt a can of Rhomar, Axiom or Fernox in
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements