I need advice on powervent shielding
140k Btu Burnham natural gas steam boiler needs to be side vented with powervent with a 14 ft run to the driveway side of the house.
The run is in the basement within the joist, which is 16 on center. The vent is single wall 3" dia stainless steel.
The plumber suggests that sheetrock be installed in ceiling to provide additional shielding.
I read online that it is best to use 24 gauge steel with gap from ceiling to allow dissipation of heat and the using sheetrock, will shield the wood, but allow a build up of heat in the area.
What is the best strategy?
Comments
-
What you readd on line, oddly enough. Drywall ("sheetrock") is not a thermal barrier — and even if it were, unless you were to use fire rated drywall — rather special stuff — it's combustible. So. Sheet metal. I'd space it out about a half inch to an inch from the joists on something non-combustible, like porcelain electric fence insulators.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England3 -
-
Not as bad as drilling the holes in the wrong place in a $9000.00 Jacuzzi tub..uh oh!!!! Mad Dog
3 -
-
-
-
Thank you all for your help. It is greatly appreciated.
It was my misunderstanding, the plumber wanted Duroc, which is cement board.
The joist bay is open, 14" wide, so there will be 5.5" inches on either side. It is a Burnham Independence 5 with PV (140k Btu). According to the manual, it requires 4" clearance, if it is in an open bay. So, it has enough clearance, but I lined it with cement board, with a gap behind it, just to make it more safe.
1
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.8K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements