Underground gas line
creger.robert
creger.robert Member Posts: 108
2” underground gas line from house to pole barn to glass making oven
Was air tested
No fittings underground
Bubbled and electrinic tested all joints
They occasionally smell gas outside by pole barn
Any thoughts
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,546
    You very likely have a leak. You need a Licensed Master plumber or gas utility worker with a gas sniffer ASAP. You could spray exposed pipe joints with a soapy water spray to see if you get any bubbles. Mad Dog
    Intplm.
  • Intplm.
    Intplm. Member Posts: 3,013
    The smell of gas is surely a concern. Call in the person who did the underground and have them fix it. And if you like, get some of this spray. It sticks nicely to the pipe and fittings. It shows a nice bubble at the leak. The other good idea is what @Mad Dog_2 says above. A soapy solution works too. I have found that the Blue stuff pictured here can find some of the smallest leaks.
  • JUGHNE
    JUGHNE Member Posts: 11,549
    Is there a gas regulator at the barn? They will sometimes pass gas thru the vent.
    ChrisJHydronicMike
    mattmia2 Member Posts: 16,742
    regulator with bad diaphragm, problem with the utilization equipment? does the diagnostic dial on the meter move after a period of time?
  • hvactech75
    hvactech75 Member Posts: 5
    If the leak is underground you should have a dead patch of grass, if they only smell gas sometimes it sounds like a purge somewhere (regulator, vent…), or a small amount may be leaving the oven prior to ignition.
    EBEBRATT-Ed Member Posts: 20,164
    Instead of looking for leaks disconnect the pipe on both ends, cap one end and test.
    Check regulator vents first as posted above,
    Any exhaust from the gas oven in the area?
    Intplm.
  • creger.robert
    yes oven exhaust is nearby