2” underground gas line from house to pole barn to glass making oven

Was air tested

No fittings underground

Bubbled and electrinic tested all joints

They occasionally smell gas outside by pole barn

Any thoughts

Comments

  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    You very likely have a leak. You need a Licensed Master plumber or gas utility worker with a gas sniffer ASAP. You could spray exposed pipe joints with a soapy water spray to see if you get any bubbles. Mad Dog

    Intplm.
  • Intplm.
    Intplm. Posts: 3,162

    The smell of gas is surely a concern. Call in the person who did the underground and have them fix it. And if you like, get some of this spray. It sticks nicely to the pipe and fittings. It shows a nice bubble at the leak. The other good idea is what @Mad Dog_2 says above. A soapy solution works too. I have found that the Blue stuff pictured here can find some of the smallest leaks.

    shopping.jpeg
  • JUGHNE
    JUGHNE Posts: 11,653

    Is there a gas regulator at the barn? They will sometimes pass gas thru the vent.

    ChrisJHydronicMike
  • mattmia2
    mattmia2 Posts: 18,399

    regulator with bad diaphragm, problem with the utilization equipment? does the diagnostic dial on the meter move after a period of time?

  • If the leak is underground you should have a dead patch of grass, if they only smell gas sometimes it sounds like a purge somewhere (regulator, vent…), or a small amount may be leaving the oven prior to ignition.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Instead of looking for leaks disconnect the pipe on both ends, cap one end and test.

    Check regulator vents first as posted above,

    Any exhaust from the gas oven in the area?

    Intplm.
  • yes oven exhaust is nearby