Damper keeps rotating to close positions

Options
efarrenovate
efarrenovate Member Posts: 6

Hi one of my customers gas slant fin gas boiler. The damper keeps rotating to the close position and lock off the boiler. It's a older model boiler and parts is difficult to find. Any

1000037360.jpg 1000037359.jpg 1000036154.jpg

Comments

  • pecmsg
    pecmsg Member Posts: 6,814

    break out your meter but sounds like a bad end switch

  • Steamhead
    Steamhead Member Posts: 18,248

    Either that or they just installed a power-stealing thermostat. I've seen this before. The small "stealing" current can make the damper malfunction. An isolation relay will fix this.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • HomerJSmith
    HomerJSmith Member Posts: 2,722
    edited January 4

    It's not necessarily in the damper that the malfunction can occur. Look at the Boiler control board connection to the damper and other connections, too. You really don't need a damper for the boiler to function. As I vaguely recall the damper defaults to open when a failure occurs. If you unplug the damper from the boiler control board, the damper should open, I think. You may have to jump the board connections to get the boiler to fire.

    "The damper keeps rotating to the close position and lock off the boiler." What is the sequence that causes this? Is the damper ever in the open position? Is the synchronous motor hot?

    Get your meter out. You could have a micro switch or relay problem.

  • 109A_5
    109A_5 Member Posts: 3,538
    edited January 4

    you could lock the damper open for heat, see instructions on the circuit board. It would not surprise me if one of the micro-switches has failed, so the circuit can't tell when the damper is in the open position.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    pecmsg
  • efarrenovate
    efarrenovate Member Posts: 6

    Thanks everyone for your input and support. I lock the damper in open position as 109 A point out. It's working so far while I am waiting on a replacement.

    Much appreciated 👏

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,721

    @efarrenovate

    Your choice of course but those dampers don't save enough $$$ to pay for the damper. The savings are minute.