45 second Trial For Ignition
Options
Robert_H
Member Posts: 273
in Oil Heating
Are there any appliances out there that still require a 45 sec. TFI?
I've found a few burners with the Carlin 48245 E Series Oil Primary Control with the jumper installed , setting 45 sec TFI. I always remove the jumper setting 15 sec. I believe the jumper is installed by default which seems negligent.
0
Comments
-
That's exactly what I would do.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
-
-
There was an alleged "technician"I was told that worked on a burner that was locking out. He took the control off and wired around it and the burner ran for a year with no issues until someone with a brain looked at it.
2