Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
45 second Trial For Ignition
Options
Robert_H
Member Posts: 258
in Oil Heating
Are there any appliances out there that still require a 45 sec. TFI?
I've found a few burners with the Carlin 48245 E Series Oil Primary Control with the jumper installed , setting 45 sec TFI. I always remove the jumper setting 15 sec. I believe the jumper is installed by default which seems negligent.
0
Comments
-
That's exactly what I would do.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
-
-
There was an alleged "technician"I was told that worked on a burner that was locking out. He took the control off and wired around it and the burner ran for a year with no issues until someone with a brain looked at it.
2
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements
