45 second Trial For Ignition
Robert_H
Robert_H Member Posts: 304
Are there any appliances out there that still require a 45 sec. TFI?
I've found a few burners with the Carlin 48245 E Series Oil Primary Control with the jumper installed , setting 45 sec TFI. I always remove the jumper setting 15 sec. I believe the jumper is installed by default which seems negligent.
    Steamhead Member Posts: 18,492
    That's exactly what I would do.
    Consulting
    EdTheHeaterManSuperTech
    EBEBRATT-Ed Member Posts: 20,164
    If any burner needs 45 seconds to light something is wrong.
    I would rather go back to a 90 second stack switch.
    EdTheHeaterMan Member Posts: 12,150
    why use a primary control at all? Ignition transformers and electrode insulators made today never fail.
    This comment is brought to you the the National Sarcasm Society.
    old_diy_guyRobert_H
    @EdTheHeaterMan
    There was an alleged "technician"I was told that worked on a burner that was locking out. He took the control off and wired around it and the burner ran for a year with no issues until someone with a brain looked at it.
    EdTheHeaterManRobert_H