BFD before the fill valve.
Excellent question and one even the folks that wrote the low lead standard cannot explain, regarding boiler fill valved needing to be LL.
In theory once water crosses a BFD that is the vented type, there is know way it could back into supply. So does any BFD need to be LL?
One could argue that if both checks failed, and someone plugged the vent port a backflow condition is possible.
Same question regarding boiler feed valves. We still see fill valves installed without BFD protection, so it is possible for that backflow condition.
The Caleffi 573 does have a spring check on the outlet, right below the gauge in this pic, basically the same check you find in most BFD. So with a combo fill/ BFD 573 on the left, you get 3 check valves and vent to atmosphere.
There are markets in the world where that check in the fill valve is considered a BFD.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks. I was looking at the non-combo Caleffi 553 with gauge. My assumption was that anything downstream of the BFD didn't have to be lead-free.
I have a Legend S-459 which isn't lead-free (planned to return in favor of a Matco-Norca BFP-90-1/2LF or equivalent that was).
My theory, and likely overthinking, is that the BFD is connected to potable water and might want to be lead-free as my "bridge." Then anything after doesn't have to be.
But, similar to an outdoor spigot, I don't see how water makes it back across as you mention, especially since I'm now looking at three check valves.
0 -
Hydronic side components do not need to be LL. But more and more brass is going LL as it is a hassle to manufacture both standard brass and LL. All the tooling in the factory needs to be changed, lubricants, machine shavings segregated, , etc.
I see some online suppliers now have a disclaimer if you but leaded brass valves and parts.
At days end it takes a fairly specific water condition to allow lead to leach out, Flint, MI for example. Most water piping and valves develop a "patina" inside within days that could prevent lead for leaching out.
But the genie is out of the bottle now, so…
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Anything after the backflow is heating pipe. Before the backflow it is plumbing.
0 -
if i am reading the michigan residential code right, only things supplying drinking and cooking water need to be low lead so the boiler feed does not need to be low lead
0 -
@mattmia i doubt any inspector will let that fly. They want anything in the potable water to be lead free.
That would mean you don't need lead free in a bathroom or outside faucet or the dishwasher, washing machine etc.?
0 -
exactly. none of woodford's stuff is low lead.
0 -
outdoor faucets are supposed yo have vacuum breakers installed. Many are built in now
DW and washers have solenoids, those would need to fail, and I think fill is above overflow level?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
clothes washer usually have an air gap built in to the inlet to the tub. i'd assume dishwashers do too but i have never taken one that far apart. but my point was that woodford silcocks are widely used and they are not lead free so it would seem that they are accepted as that part of the system is not water used for cooking or drinking(although i have seen lots of travel trailers in a driveway hooked up to a silcock).
0 -
Silcocks in Vermont are required to be lead free.
0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements