I have a single pipe steam system that is spitting condensate out of every radiator in this 3 story building. I started by flushing the boiler and cleaning the sight glass so i could verify a proper water level in the boiler. Then I checked the pressure setting and verified it was set for 2 psi. Next I suggested replacing the vents on the radiators because they were extremely old. I verified all the radiator valves were all the way turned open. I checked the pitch of the radiators and they all looked good. The radiator vents still spitt water though and the property manager is loosing faith in me. ITs doubtful that the boiler is having carryover due to water quality all the way to the third floor, but is that possible? The buildings piping is mostly concealed so I cant really check for settled piping or exactly how the piping is configured, any ideas? If the property manager doesnt kick me off the property im considering the following: disassemble several radiator valves and inspect them for dirt restriction or the rubber deteriorated and fall down restricting the valve. Is this a wise course of action? My next step would be to pull radiators, in the summer time, and powerflush the lines with a garden hose to insure the lines are clean enough to allow condensate and steam to freely flow by eachother. Your thoughts?

Comments

  • bburd
    bburd Member Posts: 1,247
    edited December 28

    how does the near-boiler piping compare with the manufacturer's recommendations for size, pitch and layout? Can you post pictures of the boiler from far enough away to see the piping, from a couple of different angles?


    Bburd
  • neilc
    neilc Member Posts: 3,129

    and what vents are on the rads now, some vents vent too fast, rads want to vent slow, fast rad venting can hold condensate where you don't want it,

    known to beat dead horses
  • mattmia2
    mattmia2 Member Posts: 15,652

    what about the main vents? how does the boiler size compare to the connected radiation?

  • kevineggerth
    kevineggerth Member Posts: 6

    I put adjustable vents on the radiators and tried setting them wide open and also on the slowest vent rate and neither stopped the vents from spitting. I dont have pictures, sorry. The near boiler pipping is done per the manual. I didnt size all the radiation to compare with boiler size but id say it is roughly properly sized and this boiler is slightly less btus than the old boiler that was in there for like 50 years. You know how a radiator valve being partially closed can cause condensate to get stuck in radiators and then spite out the vents, well im thinking a simular effect might be happening if the pipes are partially sludged up internally. Your thoughts on this as a practicle issue?

  • mattmia2
    mattmia2 Member Posts: 15,652

    what kind of variable vents? heattimer varivalves are still pretty fast at their slowest setting so if that is what you're using, you might need slower vents.

  • ethicalpaul
    ethicalpaul Member Posts: 8,177

    Every single radiator is spitting? That is strange.

    ITs doubtful that the boiler is having carryover due to water quality all the way to the third floor, but is that possible?

    It is possible. Have you been able to monitor the water line during a call for heat? If it dives that would indicate carryover.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 15,652

    if it is water leaving the boiler vs some sort of velocity issue my bet would be on priming rather than surging

  • ethicalpaul
    ethicalpaul Member Posts: 8,177

    I don’t recognize priming in low pressure steam, but just in case it can exist, what would be the cause of it and how would it be prevented?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el