2 circulators single zone

Options
zman11
zman11 Member Posts: 22

hello, my only question is, I have one thermostat and a circulator on the supply, I have a loop that needs its own circulator. Can I wire both circulators together inside the boiler wiring so whenever the thermostat calls, both pumps activate? I want both pumps to activate simultaneously all the time. On a single zone one thermostat. Do I need some kind of relay? Or just wire in parallel inside the boiler. Thanks

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,602

    I am sure it can be done but more information and pictures needed. Do you have a loop with no circulator? Doesn't sound right

  • zman11
    zman11 Member Posts: 22

    I just need to add a circulator to a loop that cast baseboard radiators. The rest is big cast iron rads. Can I have 2 circulators wired inside the boiler so both pumps work as one essentially?

  • Jamie Hall
    Jamie Hall Member Posts: 26,842

    Yes you can. Not difficult. Also pipe the pumps in parallel, so you will need piping to split the zones into two zones — and you will need to have balancing valves to get the flow riht.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England