Christmas Wishing for a Warm Classroom
Hello, all, I teach high school in a large 1930s brick school house. The building has a two-pipe steam system. The radiator for my classroom is a twenty-foot long 1.5"-2" pipe with metal fins hidden away in a sheet metal box, not unlike a baseboard heater. (Unfortunately we lost most of the beautiful cast iron radiators in the 1970s renovation.)
This radiator has not been heating more than a foot or two along its length. According to the teacher who had this room before me, this has been a problem that has persisted for many years, maybe a decade. Students have to wear their coats in class to be warm enough to study. Despite multiple requests to fix the lack of heat, the school district has done nothing to correct the problem, and for years this has notoriously been the room without heat.
Since I enjoy the steam system in my own home and reading HeatingHelp, I thought I would see if I couldn't do some simple repair myself. It seemed like the steam trap (a Hoffman 17C) might have failed closed; I thought maybe I could replace the cage unit myself. Before buying a new cage, I opened the trap. (There are shut-offs on both sides of the radiator.)
This is what I found inside ...
As you can see, it's full of debris. I cleaned out the trap out as best as I could, but now I'm wondering if the radiator (just a long pipe remember) is full solid of debris. Is it worth buying a cage? Any thoughts on how I should go about getting this radiator hot again?
Thanks,
Forest in Massachusetts
Comments
-
-
No, it seemed like metal or mineral flakes to me. There was also a fine sludge below. I didn't have any tools (except a pencil) to explore deep cleaning out at the time.
0 -
All seriousness aside:
I would take an educated guess (because you are an educator) and say that it is rust from inside the pipe radiator. Steam should not make that much rust, so it has to be from the condensate. It may have been happening since the radiator was installed.
How easy would it be to have that radiator removed by the maintenance department at the school and have it pressure cleaned? High pressure steam or water with a gritty mix forced thru that pipe radiator might be needed. You may need to take it off site somewhere?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
-
does it heat if you dig that stuff out, put the lid on the trap and turn the valves on? don't leave it that way because it will put steam in the returns but it will tell you if it is working. how high above the boiler is that? that stuff might have been washed in there if the system flooded for some reason.
1 -
-
I was thinking of making home made wine using raisins so I didn't need to age the grape's juices for so long!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Great detective work.
I applaud you for taking the initiave to help heat your classroom. I doubt the students can learn properly in that enviroment.
I would take some picture and then I would drag maintenance, the principal and the school superintendent down there and stick their nose in the trap.
I know I am a harsh old man and you have a job to keep but seriously I hope they fix it.
I would have a chat with the principal and show him the problem. Christmas vacation is coming up and they should have maintenance fix this during vacation or call a contractor in that will fix this.
I am a MA taxpayer and they need to get this fixed.
6 -
can you borrow a shop vac and suck that out? doesn't look like there's any pressure under that trap body, make sure both ball valves operate in case you find some steam pressure, then if you're worried about sending steam thru to the returns, consider sacrificing the supply ball valve and setting it mostly closed to operate as a quasi orifice, throttle your heat if it flows at all,
known to beat dead horses1 -
Thank you all for your helpful thoughts and suggestions.
@mattmia2 My classroom is only one floor above the boiler. I'd like to think the debris was the result of a one-time flood, not a chronic problem.
My initial cleaning out of the trap today didn't get the steam flowing, but I didn't have anything but pencils and wrenches at hand. I'll bring some better tools for cleaning the trap tomorrow and see if we can get some steam flowing through.
I'm afraid the school wouldn't look kindly on what would be seen as "tinkering" with school property, so I'm reluctant to share this investigation with the principal or superintendent. But if I can fix the radiator with some knowhow from you all and little work on my part, I still feel I ought to try.
1 -
@Forest.
I understand the spot your in.
Back in the day (78) I took a night class to get my electricians license. The instructor used to open the windows and lock the door and hang a newspaper over the door window. We would smoke butts all during class
0 -
Unfortunately it seems that the radiator (a pipe) is also blocked up to an unknown degree by sludge and mineral flakes like fine crushed stone.
Here's a picture of the existing cage unit. I was expecting a spring with it, but there was none. Is that normal?
0 -
the cage unit looks ok, the bellows expand out the bottom and close the seat. the spring is probably more a way of making a few cage units fit a bunch of different proprietary body designs by changing the spring.
are you sure the boiler was firing and if there is a zone valve, that was open during your test? that seat is the smallest part of the return piping so debris that got past there probably didn't block it up.
you can also try opening the supply with the cover off and see if steam gets in to the emitter and works its way to the trap.
you could have the pitch of the piping trapping water in the supply blocking the steam or in the return keeping the air from getting out of the emitter.
1
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 428 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements