philosurfer
Member Posts: 2
0
Comments
-
-
-
Wait a second, that last picture in the photo series. The boiler is off screen to the RIGHT, but that middle pipe, which feeds the hammering radiator, is pitched slight at the joint to the left (you can see it leaning on the bottom pipe). I wonder if I simply raise that up a tad, maybe it would fix water hammer?
0 -
Try turning that vent to its slowest setting. Even the slowest setting on a vent rite is pretty fast if i recall, might need to put a slower vent on it.
0 -
What vent was on the radiator before?
Also it looks like the dry returns all connect together at the boiler above the water line, that is incorrect and can cause a number of problems but might be sort of ok.
0 -
It might indeed. In fact, that might be the whole problem…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.8K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements