heat pump water heater with domestic coil backup
Next year I'm considering installing a 50 gallon hybrid electric heat pump water heater and abandoning the domestic coil in my nearly 30-year-old Burnham V7 steamer. However I would like to see if somehow I could still use the domestic coil for a backup should the HPWH have high-tech issues. How would I pipe it and how would I control the burner to choose whether the boiler is either warm start or cold start?
Unit I'm planning on installing :
Current domestic coil piping:
I don't know why the installer piped the hot out from bottom when it should be coming out of the top.
Planned installation spot :
House used to have I believe it was an 80 gallon regular tank electric water heater so I already have a 30 amp circuit that is run to that spot and is dead ended inside of the panel and I've already run 3/4" pex to the sump pit for the condensate drain from the HPWH and I've run it along the steam system wet return. I have already done some checking and the wet return only ever gets warm to the touch during an extended call for heat.
how low can the aquastat be set for the tankless coil? if you can set it below ambient then that will turn it off. otherwise you can put a toggle switch in series with it.
you can pipe it in parallel and it will be one or the other or you can pipe it before the tank and it will het the water before it gets to the tank if the boiler s hot. you would need a bypass for the tank if you want to use it in place of the tank.
So the model that's installed appears to have two temperature ranges. 40 to 180° f or 100 to 240° f, so I think for simplicity if I do go the route of including the domestic coil in the new hot water loop I'll just do a switch in the aquastat wiring or I can even just pull it off of one of the T terminals on the primary control if I don't want to use it and have the boiler as a cold start.
Per the advice of @Intplm. , I'm going to run the HPWH as a standalone unit. Drew up a quick piping diagram today as well. Even though I am on well water with a 32 gallon pressure tank, the manufacturer still wants an expansion tank by the tank.
Hi, Here's a quick sketch of how I like to valve things. HPs like cold water, so I'd put it first, then you have the coil as backup if needed. The three valve approach has been around a while for isolating and bypassing equipment.
Yours, Larry
Thanks gents however in the interest of simplicity I'm going to not even include the coil in the piping. Just straight into the HPWH with a tee for the boiler fill and a tee for the expansion tank
Re drew my piping diagram
Will a 50 gallon tank be adequate for your needs? Recovery is very slow, depending on incoming water temperature, once you deplete the tank.