Is it a bad idea to use galvanized pipe and fittings in a closed-loop 100% water hydronic system?
I stumbled into a bunch of galvanized fittings and pipe from an auction. Even some large 2" diameter ones to potentially make-up a "short and fat" header for a 3-pipe buffer tank setup for my heat pump hydronic system.
I've read how black iron should be used instead of gavanized, but how much am I really risking in future issues with my non-glycol, naturally soft water (I'm in the moutains of Colorado, so it's all snowmelt) in my hydronic system?
Comments
-
It has been my experience that galvanized steel piping corrodes (rusts) incredibly fast. Black iron doesn't.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
my understanding is the concept of dissimilar metals copper and zinc, with an electrolyte can cause corrosion
In an open loop system you need a dielectric union or nipple between the two different metals
You could use a brass nipple between the copper to galvanized connection
Galvanized into the tank Is not an issue , if you use brass iso flanges on the pumps you are covered
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks, guys!
0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 394 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements