Poor venting- and then added two Big Mouths

Options
GW
GW Member Posts: 5,133

Did a boiler job/ venting was dismal- 1/8” nips and 90s leading to tiny vents, on the various drops into the wet return.

We found a spot where an on rad had been pulled and capped. We slapped on a couple big mouths. It’s maybe 30 feet from the boiler.

With Old tiny vent that may or may not be working:

8:35 to get the steam from boiler to the “capped takeoff” (the main- one can certainly feel the steam coming through)


with the two big mouths:

7:29.

I guess a minute plus savings is good, I thought it would have been faster

Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • Steamhead
    Steamhead Member Posts: 18,146

    Sure the Big Mouths are working?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,483

    Has the boiler been properly cleaned? Wet steam will slog along, considerably slower than dry steam.

  • GW
    GW Member Posts: 5,133

    @Steamhead im not sure- I settled for the one minute faster and called it a day. If you can tell me how to quantify the venting please let me know

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • GW
    GW Member Posts: 5,133

    @STEAM DOCTOR its a new boiler, I’ll go back and skim early next week. So the two results were like for like as fast as the boiler goes

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,483

    Would not be surprised, if venting time increases after skimming.

    GW
  • Jamie Hall
    Jamie Hall Member Posts: 26,679

    8 minu tes measured from when? When the burner starts, or when the header sees steam? If it's from when the header sees steam. that's slow (I'd have expected 2 to 3 minutes). From the burner start?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • GW
    GW Member Posts: 5,133

    Jamie, when the header is steamed. I’ll skim it and report back

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • dabrakeman
    dabrakeman Member Posts: 819

    Cold or warm pipes?