Poor venting- and then added two Big Mouths
Did a boiler job/ venting was dismal- 1/8” nips and 90s leading to tiny vents, on the various drops into the wet return.
We found a spot where an on rad had been pulled and capped. We slapped on a couple big mouths. It’s maybe 30 feet from the boiler.
With Old tiny vent that may or may not be working:
8:35 to get the steam from boiler to the “capped takeoff” (the main- one can certainly feel the steam coming through)
with the two big mouths:
7:29.
I guess a minute plus savings is good, I thought it would have been faster
Comments
-
Sure the Big Mouths are working?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Has the boiler been properly cleaned? Wet steam will slog along, considerably slower than dry steam.
0 -
@Steamhead im not sure- I settled for the one minute faster and called it a day. If you can tell me how to quantify the venting please let me know
0 -
@STEAM DOCTOR its a new boiler, I’ll go back and skim early next week. So the two results were like for like as fast as the boiler goes
0 -
-
8 minu tes measured from when? When the burner starts, or when the header sees steam? If it's from when the header sees steam. that's slow (I'd have expected 2 to 3 minutes). From the burner start?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie, when the header is steamed. I’ll skim it and report back
0 -
Cold or warm pipes?
0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 394 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements