Poor venting- and then added two Big Mouths
GW
GW Member Posts: 5,184
Did a boiler job/ venting was dismal- 1/8” nips and 90s leading to tiny vents, on the various drops into the wet return.
We found a spot where an on rad had been pulled and capped. We slapped on a couple big mouths. It’s maybe 30 feet from the boiler.
With Old tiny vent that may or may not be working:
8:35 to get the steam from boiler to the “capped takeoff” (the main- one can certainly feel the steam coming through)
with the two big mouths:
7:29.
I guess a minute plus savings is good, I thought it would have been faster
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
    Steamhead Member Posts: 18,468
    Sure the Big Mouths are working?
    Consulting
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,587
    Has the boiler been properly cleaned? Wet steam will slog along, considerably slower than dry steam.
  • GW
    @Steamhead im not sure- I settled for the one minute faster and called it a day. If you can tell me how to quantify the venting please let me know
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • GW
    @STEAM DOCTOR its a new boiler, I’ll go back and skim early next week. So the two results were like for like as fast as the boiler goes
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • STEAM DOCTOR
    Would not be surprised, if venting time increases after skimming.
    GW
    Jamie Hall Member Posts: 27,324
    8 minu tes measured from when? When the burner starts, or when the header sees steam? If it's from when the header sees steam. that's slow (I'd have expected 2 to 3 minutes). From the burner start?
  • GW
    Jamie, when the header is steamed. I’ll skim it and report back
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • dabrakeman
    dabrakeman Member Posts: 1,003
    Cold or warm pipes?
