Decoupled buffer tank (four port)
I'm trying to understand how controls work for a four-port buffer tank. The right side seems straightforward - thermostats and switching relay have zone circulators turn on and "call for heat" isn't needed since the water tank is always hot (goal is 140F-180F as panel radiators are designed for 160F at present).
How are the aquastats set up to maintain the buffer tank temperature? I feel like I'm missing something simple.
    hot_rod Posts: 28,705
    Do you have this piped yet? There is a better option for piping a buffer if you are interested?
    A 3 pipe buffer allows direct to load boiler, tank only heats when load(s) are off. As such you are not flowing across the tank.
    As for control. Some boilers include an extra sensor the could be used as a system sensor. Manual indicates DHW sensor is optional;, maybe a boiler sensor also? It's probably the same sensor for either DHW or system. It just reads a temperature.
    That sensor goes in, or on the buffer tank, mid point. It tells the boiler to maintain the tank temperature.
    If you use ODR the tank will be held at a temperature based on the outdoor temperature.
    A basic relay box, ideally Caleffi ZSR :) for the 3 pumps,
    In this case the relay box does not fire the boiler, the boiler only sees the tank sensor as it's call for heat. Come warm weather the ODR should shut 'er down, tank goes cold.
    Here is the control wiring for the Laars, lower right shows the system sensor connection.
  • Kaos
    Kaos Posts: 1,003
    edited November 2025
    Why are you connecting a 200k unit to about 50k of panel rads?
    A right sized modcon with either heat pump water heater, power vent tank or indirect would cost less, be WAY simpler to install, take up about the same space and be more efficient.
    P.S. Panel rads with a mix of TRVs/zone valves/ always on zones, piped direct to load on a right sized modcon is a great combination.
  • Nothing plumbed or ordered yet (except I ordered one panel radiator and some hePEX).
    I will read more into the 3-pipe option. I think the "DHW sensor" is for the DHW recirculator setup. Does the buffer tank aquastat get wired similar to an aquastat on an indirect tank?
    It's actually a 7-zone setup (I took a shortcut on the diagram) - perhaps overkill, but the house was originally set up as electric heat, so there's insulation in all the interior walls and between interior floors. Plus I was concerned that the fireplace insert would throw off a single-floor thermostat when used.
    7 zones, what is the total btu load?
    That is a 185,00 output boiler, quite large for most residential applications
    True, you can lock it down probably a 10-1 turndown?
  • CoolCalc says ~51,000. That particular model only comes in that size plus I want the combi (limited space for indirect tank) and have well water. Smallest zone just under 3800.
    The boiler needs to size to the largest load. In some cases the DHW is the largest load.
    Once you define how much or how quickly you want hot water. I doubt most people think about that, until they don’t have enough hot water.
    The 199 could give you 4-5 gallons per minute based on 50-55 well water at a 77 rise. So itwould keep up with a standard 1/2 tub filler, or two showers running.
    You use hot water differently with a combi or tankless.
    With any tank type you fill a tub or run hw until it runs too cold, wait for it to recover. With a combi it just keeps providing as long as you want to feed it gas or lp.
    DHW production tends to taper off as the HX gets scaled, add the flush valves, knowing that you will be descaling based on water hardness and how many gallons pass through
    As far as the heat side sizing and buffer option.
    Look at the smallest zone load. How does that match the lowest turn down? That is one way to determine if a buffer adds value.
    Regardless, combis do cycle a lot. Anytime any hot water faucet is opened it will fire
    My mother in law would hand wash and rinse dishes. She was old school, didn’t trust an automatic dishwasher. My father in law did sort of trust the DW, but would hand wash the dish before putting it in!
    With every dish they would turn the faucet on and off. So the Laars Mascot combi probably cycled 1000’s
    , maybe 10’s of thousands of times. It ran without any problems for 16 years, on LP
  • Buffer is needed - smallest zone is 3753 and largest is 11214. The unit's 10:1 turndown gives me a low output of 18,500.
    My dishwasher is from the 1990s and cleans almost anything, but I see your point.
    the buffer tank for a modulating boiler will be much smaller than a non mod boiler.
    Here is some sizing math.
    You will want a tank with 1-1/2 or 2” taps. Boiler Buddy, Lochinvar, Laars.
    Zilmet has some small wall hung versions.
  • Kaos
    Kaos Posts: 1,003
    If you must have go the buffer route, you have two options for control. You can set up the modcon to constant circulation, no need for any sensors or connection to your zones. The modcon will automatically fire to maintain the target supply water temp when any zones come on-line and cool down the buffer.
    The other option is to have a remote sensor in the buffer and have the modcon maintain that temperature. Again, no controls connection to your zones is needed.
    In either case the important bit is to set up a decent outdoor reset curve, you only want the modcon to supply that 160F water when at your outdoor design temp, the rest of the year it can be much less which significantly increases the efficiency of the boiler.
    Well water can be hard which make any instant water heater a maintance issue. If you have space for a floor mount plus a 25-30 gallon buffer tank, you can easily fit a low boy indirect/power vent with a wallmount modcon above it. There are also wallmount indirects you can put above a floor mount boiler.
    There are several goals a buffer can accomplish.
    On a conventional boiler, say a wood or pellet fired we would run the tank to 180F or higher. A long hot, efficient burn.
    Pull radiant loads off via a mixer on outdoor reset. So now you leverage maybe a 100° ∆.
    On a condensing boiler it is more about lessening the cycling than a long drawdown. The ODR limits the tank temperature.
    Really all you are doing is turning a low water content boiler into a higher water content boiler, with two components. AKA a condensing tank water heater :)
    That was the attraction to the Polaris, Hydropulse, HTP voyager and Phoenix and others. The buffer was built in. They work great with even only 5-1 turn down.
  • I have a softener on the well to help with hardness - I recall seeing that make-up water should be after my filter but before the softener. The domestic hot water inlet would use softened water.
    Buffer tank calculation:
    t = 10 minutes
    Q_hs = 18,200 Btu/hr (lowest turn-down of boiler)
    Q_loadmin = 1500 Btu/hr (assume a future towel warmer)
    ∆T = 40°F (140°F - 180°F)
    I'm not seeing a system sensor input on the boiler I'm looking at. I see a thread for using a Tekmar 256 for dynamically setting buffer tank temperature, but I'm not following how that modulates the boiler, other than also having a boiler-connected outdoor reset.
    Tekmar 306P and equivalent seem to be able to modulate the boiler but that's a different type of thing it seems.
    If you run ODR, the boiler just needs a call for heat and it will modulate. Just jumper TT connection on the boiler.
    I see the system sensor connection on the board, #6 & 13. Perhaps this is the sensor in the boiler. Or is it intended for an additional sensor?
    As @Kaos mentioned, you could wire the boiler pump to run 24/7. Or tie it in to a relay to go off when ODR turns the boiler off, around 68° typically.
    Yet another option wire any setpoint control to the boiler, run the tank to a specific temperature. Skip the ODR just run the tank to a specific temperature.
    My first choice would be to let the boiler control run the tank temperature if the board allows that?
    I don't see Laars offering a separate sensor in their option kits, however.
    Or buy a boiler like the Lochinvar Knight that give you a row of additional sensor connections. #23 & 24 is what I have in my buffer. You have connections for flow switches, LWC, three different heat calls, power for louvers, variable speed input. Most any option you can think of.
    Pretty much all the higher priced mod cons have a more robust control. More adjustments, more input options.
    My Lochinvar did come with a spare sensor. It is a universal sensor. The sensor can be placed anywhere, in a tank, on a pipe, it is just a thermistor. The only unique sensor is the ODR, it is in a weatherproof enclosure
    I have done a number of small buffers with electric tanks, here is a 6 gallon and maybe a 12 or 20 gallon.
    I leave an element in for backup should the boiler go down I still have some heat.
    The small Lochinvar electric tanks have a bunch of ports you can use,
    3rd pic shows fittings to increase the 3/4 ports to 1-1/4 or 1-1/2"
    Screenshot 2025-11-16 at 2.28.32 PM.png Screenshot 2025-11-16 at 2.29.19 PM.png Screenshot 2025-11-16 at 2.30.05 PM.png
  • Thanks - maybe Lochinvar is the way to go. The Lochinvar NCF199N is ironically less locally than the Bradford White. Someone I know in HVAC says to get Navien because "that's what everyone is installing" though I've heard that Lochinvar's quality is better (along with Laars / Bradford White). I was intrigued by the Laars mini-indirect inside the unit for DHW, but I also remember reading that Lochinvar solved the "cold water sandwich" as well.
  • Kaos
    Kaos Posts: 1,003
    Check what models your local distributors stock spares for. You want to get something you can easily get replacement parts for in a pinch.
    You have to be careful with add on bits, it doesn't take much to add a couple of grand of BOM cost to an install.
    The continuous circulation setup feels wrong at first glance but it works very well, it is what I run with my AWHP. Simple to set up and control, all the bits for setting it up are built right into the boiler. An ECM pump is a good idea for this type of setup. With decent outdoor reset, proper fire limit and delta T limits on the boiler you can get nice long burner runs at low fire.
    Sounds like you are also micro zoning. There is usually no need for this, lot of the zones can be plumbed always on which increases the effective min zone size. Find areas that you want extra toasty, I run my bath floor floor heat, towel warmers and rad by the entrance always on. This also saves cost as there is no need for controls there.
    For the rest of the house think about places where you actually want programmable thermostat control and where it can be TRVs. For example a spare bed is a good place where a TRV is good enough. You can also group zones with similar solar gain together under a single thermostat.
  • I wound up getting the Bradford White BFTCF199NA3XN (-1XN in earlier revisions) and a Zilmet ZBT-21 since going to 30-gallon did not seem necessary (21-gallon is likely too big). It came with 1-1/4" ports, not 1-1/2" ports like the other brands (I forgot that hot_rod recommended larger). The boiler is oversized on the heating size due to DHW load and lack of basement space pushed me to the combi (68,000 BTUH of panel radiators on a boiler that will modulate between ~19,900 and ~199,000).
    Flow to the panel radiators is small (<6 GPM) even with all running at once.
    I thought that I could go 1-1/4" boiler piping (8.2 - 16.3 GPM for 2-4 ft/s) to the buffer tank, especially with:
    GPM = BTU / (Delta T * 500) = 68000 / (20 * 500) —> 6.8 GPM (seems the max would be 163,000 BTUH)
    I just found this in the installation manual - I don't read this as a minimum 1-1/2" piping (at least in the left column, though "CH pipe size" is mentioned in the right column). Seems like 1-1/4" is fine for this design.
    Here are some guidelines, based on flow rates and velocity. It is not cast in stone if you are off by a few gpm, not a dealbreaker.
    This was for a 20 gpm flow on the B or distribution side.
    If your distribution is 6.8 gpm total, then 1-1/4' is plenty.
    Same concept for near boiler piping on zone pumped systems.