Gas Pressure Adjustment for Electronic Igniter

Options
Lexi_2019
Lexi_2019 Member Posts: 1

Hello Team Member

,
I have a Carrier furnace model 58GS100-3. It is in good condition. The problem I have is the electronic pilot is on or have spark but the gas is not on. This happen intermittently. I do have 24 Vac on the gas wire and pilot light wire. I hear the gas valve is turning on. If I use a lighter the furnace will turn on. My question is, how do I increase the gas pressure on my gas valve. The model for the gas valve is 301273-705. Do I need a manometer for this procedure. Can I do this without a manometer? Where do I adjust for more gas pressure? I have attached files for reference. Your help is greatly appreciated.

Regards,

Lexi_2019

Comments

  • mattmia2
    mattmia2 Member Posts: 15,067

    if you light it manually (which i do not recommend for several reasons), does the pilot light, prove flame, then light the main burner or is your extra flame providing the flame rectification to prove the pilot?

  • 109A_5
    109A_5 Member Posts: 3,259

    " This happen intermittently "

    So when it works correctly the pilot is fine ? If so changing the pressure probably won't help, sounds like the pilot valve is intermittently bad. If the pilot flame is just constantly low causing intermittent operation the pilot orifice maybe partially clogged and needs cleaning.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Member Posts: 15,067

    or the wire to the electrode or the electrode itself is shorting to ground and not lighting the pilot burner or something is wrong with the high voltage circuit in the ignition control.