Gas Pressure Adjustment for Electronic Igniter
Hello Team Member
,
I have a Carrier furnace model 58GS100-3. It is in good condition. The problem I have is the electronic pilot is on or have spark but the gas is not on. This happen intermittently. I do have 24 Vac on the gas wire and pilot light wire. I hear the gas valve is turning on. If I use a lighter the furnace will turn on. My question is, how do I increase the gas pressure on my gas valve. The model for the gas valve is 301273-705. Do I need a manometer for this procedure. Can I do this without a manometer? Where do I adjust for more gas pressure? I have attached files for reference. Your help is greatly appreciated.
Regards,
Lexi_2019
Comments
-
if you light it manually (which i do not recommend for several reasons), does the pilot light, prove flame, then light the main burner or is your extra flame providing the flame rectification to prove the pilot?
0 -
" This happen intermittently "
So when it works correctly the pilot is fine ? If so changing the pressure probably won't help, sounds like the pilot valve is intermittently bad. If the pilot flame is just constantly low causing intermittent operation the pilot orifice maybe partially clogged and needs cleaning.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
or the wire to the electrode or the electrode itself is shorting to ground and not lighting the pilot burner or something is wrong with the high voltage circuit in the ignition control.
0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 394 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements