Water loss
I have a customer that has 3-300 HP boilers with a 2 pipe steam system. All of the condensate is returned to a boiler feed tank where the only common connection between the three boilers is on the steam supply to a main header. The problem I have is when draining 1 boiler the boiler next to it looses water rather quickly and locking out on the manual reset LWCO. Also after correcting a problem with the burner modulation circuit where the burner was only firing in low, I put the burner back into auto and when it went to high fire the same thing happened with rapid water loss.
The 3 supply’s do enter the main header at the top and the traps at the ends of the header lift the condensate about 3 feet to get back to the boiler feed tank. The bottom of the main header is about 6” above the water line of the boiler.
Comments
-
Hmm. Seems the two boilers are acting as one when draining. Is the condensate return tank working properly? Is the float and pump adjusted correctly?
0 -
Are there individual check valves on the feed lines from the condensate tank boiler feed pumps to the boilers? Are they working?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I would like to see the return piping. Connecting multiple boilers together below the water line (without a check valve(s)) is against code.
If your feedwater piping from the pumps to each individual boiler two check valves are required by the ASME code. 1 at the feed water pump and 1 at the boiler.
Those checks are probably bad unless you have some improper piping going on
0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 394 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements