Replacing fuel line from bottom to top
replaced filter and nozzle was not getting fuel valve on bottom of tank will not open. Ran 3/8s copper pipe & fittings it fired up after bleeding then quits would putting an inline filter line filter do any good? I think it’s getting air somewhere can’t get a solid stream of fuel. The tubing is flared so can I put pipe dope tape on it to help stopping the air.
Comments
-
You ran a new fuel line out of the top of the tank, and connected to where? Did you connect to the existing oil line at the tank (after the bad valve), or did you connect at the burner somewhere? Exactly where? Pics?
Is the new oil line going straight down? How far off the bottom? Sludge?
If the flare is good, the pump should prime.
0 -
ran the fuel line from the top of the tank to the furnace. Line goes 41 inches into tank not touching the bottom. Getting air somewhere would it help to put an inline filter and maybe some pipe dope on the fittings?
0 -
Filter won't help at all. As to the fittings — any fittings on an oil line — particularly one running a vacuum as a top withdrawal does — must be well made flares. And, for that matter, avoided if possible.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You need Firomatic valve and an oil filter at the tank and a Firomatic at the filter to meet code. Maybe an OSV valve. If you pulling air you have a suction leak. Period
With the tubing in a vacuum you probably will not see an oil leak.
0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements