Gas Odor after Boiler Shuts Down
Bridgestone
Bridgestone Member Posts: 29
I have a problem with a lingering gas odor after my boiler shuts down. The model is a Weill McLain CGi-5. There is no gas odor before the boiler starts, or when it’s running. The odor occurs only immediately after the inducer-fan shuts down, lasting 4 to 5 minutes. As the gas odor moves up the stairwell it slowly diminishes.
A technician from the gas company came and used his gas detector. It turned red for 1 second and then went off. His diagnosis was “ likely gas valve bleeding through”. He did not red-tag the boiler. Using his words I called Weil McLain and under warranty they provided a new gas valve. The heating tech left shortly after installing the new valve, both of us assuming the problem was solved. To my dismay the odor problem remains the same.
Before I have the technician come back I would like to get some input on what the problem could be. I should note that the inducer runs for about 14 seconds after the “flame” light” on the panel goes off. During those 14 seconds I don’t smell gas at the boiler, only right after the inducer stops running.
Any thoughts on what could help diagnose the problem would be appreciated.
    EdTheHeaterMan Member Posts: 11,748
    edited October 2025
    This is going to be a process of elimination thing. You now know that the replacement gas valve did not solve the problem. Your technician needs to look further. Without actually being there, It is hard to say exactly where the odor is coming from
    HVACNUT Member Posts: 7,305
    Does the inducer vent into a chimney, or sidewall? The 15 second run time when the cycle is complete is post purge. The very purpose of it is to expell unspent gasses from the system. Start looking for flue or HX obstructions.
    EBEBRATT-Ed Member Posts: 19,881
    Do you have any exhaust fans running in the house? The house could be under negative pressure compared to the outside. Someone needs to decide if theis smell is unburned natural gas or fumes from combustion
    EdTheHeaterManSuperTech
  • Bridgestone
    The inducer vents out a sidewall. There are no exhaust fans running in the house. Given the strength of the odor, I think its fumes from combustion, but not sure. Since there is no odor when the boiler is running I would think that its venting properly. I wondering if the post purge time can be extended, maybe that would help.
    mattmia2 Member Posts: 15,984
    edited October 2025
    watch what happens to the burner as it shuts down, it shloud go out quickly. maybe the gas valve is slow to close.
    check the manifold fittings after the burner with soap too, make sure it isn't leaking such that it gets burned off while it is firing but leaks out after it shuts down
  • Bridgestone
    Thank you for your comments. The tech guy came, tested the boiler and did fall maintenance. He stated that the odor I smell after the burner and inducer shut down is combustion fume, not gas. The post purge of the inducer cannot be extended beyond 15 seconds. There was nothing else he could do to improve the situation. I'm satisfied that there's no danger from the fumes and have decided to live with the odor as the fumes dissipate. The boiler is located in a large basement room so shutting the door to that room and another at the top of the basement stairwell will help.
    @Bridgestone You could easily install a time delay relay to extend the purge regardless of what your technician told you.
    You shouldn't be getting that backdraft and if It was my house I would investigate further.
  • Bridgestone
    Prior to the technician visit I had called WeilMcLain. The Rep didn't have an answer as to what might cause the fume odor, but suggested that the technician call WM when he arrived. Instead the Tech called his supervisor and did annual maintenance, but declined calling WM. Referring back to my conversation with WM, the Rep said (as best as I understood) a possible cause was a small leak at the inducer motor/venting connection causing a small amount of remaining fumes to escape after the post purge was complete. He thought that while the inducer was running the leak was not letting fumes escape.
    I'm wondering if the motor/venting connection is something that is plausible and worth pursuing.
    I'm considering calling another technician who's been recommended as very experienced with WM boilers.
  • Bridgestone
    Perr-y32 - If I understand correctly, was the gasket you referred to between the inducer fan housing/outlet and the vent pipe connection point? How long did it take to replace the gasket? I'll likely have another technician investigate the matter, but wait until spring if it's a large repair.
  • HomerJSmith
    HomerJSmith Member Posts: 2,743
    Pics always help in diagnosis. I would want to see the combustion (outside) air openings, the direct venting outside the building, whether the outside vent is on the Windward or Leeward side, the gas pressure at the boiler (Nat or LP), the boiler operational altitude, has your boiler had a combustion analysis done, among others.
    It is not uncommon for homeowners to confuse combustion gases for Nat or LP gas leaks. I would suspect that what you are smelling is combustion gases.
    It is not uncommon for installers to mis-install direct venting. I've seen a lot of it.
  • Bridgestone
    Thanks for your input. It is combustion gas. The gas pressure at the boiler has been checked and a combustion analysis has been done. The is no combustion gas odor while the boiler is running, or during the 15 second post-purge. The odor leaves the boiler for about 3-4 minutes after the post-purge is complete, slowly diminishing. The boiler was installed almost 3 years ago. I first noticed the odor about 1 year ago. I've noticed that the inducer motor vibrates some but the installer said that's normal. Attached are pictures. The venting is 4' up and 8' out.
    @Bridgestone
    2 things.
    Check the manual. I don't think the tee outside the house is installed properly it need to be vertical. Also, too low to the ground
    The hose coming off the tee indoors for the condensate does it have a water trap on it? It needs one.
