Correct placement of circulator pump
JBB
JBB Member Posts: 24
Hello, I have a question regarding the placement of a Taco circulator pump. Mine is a radiant underfloor system using a 40 gallon gas water heater as the heat source. I had to replace it, and the pump, they were both over 10 yrs old. The flow direction is IN at the water heater drain, and OUT at the hot side of the top of the wh. Should this be piped out at the bottom, and in at the wh top? This is a closed system, with an expansion tank on the wh top cold pipe. JB
Thanks for the help!
    Jamie Hall Member Posts: 27,225
    Direction of flow through the tank isn't that critical — it's forced flow, so having the hot outlet at the top isn't that important.
    What IS important is where the expansion tank is relative to the circulator: the expansion tank should be connected a foot or two upstream of the INLET to the circulator.
  • JBB
    Thanks; So the expansion tank should never be instaĺled on the cold water inlet side of the water heater at all?
    hot_rod Member Posts: 27,308
    is the water heater supplying hot water fir the building ? Or is it dedicated to the radiant?
  • JBB
    supplying hot water to the radiant underfloor system only
    the pump can go on either supply or return piping
    What is important in the expansion tank should be on the inlet side of the circ, regardless of the pumps location
    The air purger always goes at the hottest point in the system, right out of the heater/ boiler
    See examples
    GGross
  • JBB
    Thanks; that is exactly how mine is set up!