Vacuum taking a long time to stop dropping
Hey guys
Just wanted to check something with someone with more experience than myself...
Did a dual zone mini split install yesterday. Lines are 11 and 22 feet approximately.
Pulled a vacuum down to 240 microns, locked off the ball valve (Appion valve core removal tool) and the pressure continued to VERY slowly rise for a good 30-40 minutes, up to mid 300's..
Tried vacuuming several times in the end, and on the last one left it longer. It went from 240 to 360 in the first 40-45 minutes, and then stayed solid at 360 for a further 25 minutes. So finished the job.
But I've not experienced such a slow rise before, and taking so long to finally settle.
Is this fairly common, anyone else here experienced similar?
Thank you!
moisture is evaporating.
What's the longest period of time that's typical for the pressure to stop rising and lock in?
Is 45 minutes unusual/particularly long?
Yes, this is precisely what I've found in the past too. Sub 20 minutes to stabilize.
Should I have any concerns that this one took around 45 minutes?
Yes, it stopped at 360 which was great.
I guess the only thing that concerned me was watching it rise for 45 minutes, a rise of 10 microns every approx 8 minutes. I left it 25 minutes locked on 360 microns, just concerned if I'd have waited longer it may have risen again?0 -
if there’s moisture in the line set then it will slowly and continually rise to above 1000 µm
So after stabilizing for 25 minutes this would have been very unlikely in my case?
So if it were any kind of physical leak, the rise would have been much higher\quicker?
Awesome, that's what I thought and a big thank you for confirming. Will put my mind at rest, lol 😊
Like I mentioned on the first post, really wanted to get the opinion of people with more experience than myself, and got precisely that.
Great forum, thank you everyone! 👍️
maybe it is something other than water evaporating.
What makes you say that out of interest? That it took 45 minutes to stabilize? What time do you usually expect for stabilization?
i'm not very experienced with evacuating systems with a micron gauge but oils and solvents and things like that will also evaporate and will have different vapor pressures than water.
Yes, mositure was covered by pecmsg (above). Oils and solvents, I think unlikely as it was all brand new lines fitted with protective end caps to keep contaminants out. But possible I suppose?
maybe contaminants leftover from manufacturing or not the best quality refrigeration oil from the factory? I guess the compressor was isolated so the factory oil shouldn't be involved.
Yes, compressor was isolated. Not sure on the others, but anything is possible I guess.
- 87.8K THE MAIN WALL
- 133 Chimneys & Flues
- 79 Pipe Deterioration
- 396 Solar
