Replacement ceiling diffuser for heat pump

I'm thinking about replacing a central air system with a ducted heat pump. The existing A/C system has ducts in the attic (which I plan on re-using for the HP) and diffusers in the ceiling. There is a single return in the ceiling in a common hallway. The diffusers are very similar to the attached image. These work fine for A/C in the summer, but I am concerned they won't be as effective for heating. Is there some kind of hybrid diffuser with the same footprint I can look at that would serve both cooling and heating? I'd prefer to re-use the existing ceiling holes and not cut new ones if I don't have to. This is for a home in the Hudson Valley of New York state. Existing heat is hydronic with an oil-fired boiler, which I still intend to use on colder winter days. Thanks.
Comments
-
The existing diffuser type doesn't matter, what you want is the duct size behind it.
With ceiling register and for heat to work well you want something with decent throw straight down, you have to get the air down to floor level to mix. You also have to watch where people will sit as you don't want to blow air directly at people.
I used regular adjustable commercial grills from our local supply house, something close to this:
Important bit when doing this type of hvac work is to get a duct blaster test and make sure the new install is reasonably air tight. Air leaks in attic mounted units can be a big source of heat loss, around the neighborhood of 25% is common, a bit of air sealing now has a big return on operating cost.
0 -
Overhead heat especially with a lo temp heat pump will not work well when it is cold. It might be ok in the spring and fall.
0 -
If the diffuser shown is what you have, then its more than just a diffuser replacement. What you're showing comes as a combination register/boot so replacing the diffusers will also need new boots.
0 -
That was definitely the case with older single speed heat pumps. Newer cold climate units deliver rated capacity down to 0F is some cases, that means the supply temperature does not drop even when cold. I have a cold climate unit up at the cottage where -15F is common and the air coming out of the unit is well above 100F even on the coldest nights.
Speaking of which, @wlee make sure they install a unit with vapor injection (hyper heat, cold climate etc.).
0 -
I'm not familiar with vapor injection, can you expand on it a bit? Is it a feature unique to a particular brand?
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.6K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 47 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements