I was talking with a contractor installing one of the boilers I sold and asked if he was going to use Megapress He said he would on the large fittings but not on the smaller ones. I thought it was the cost but he said the small fittings are only rated for only 5 psi. Is that true? Are the small fittings only rated for 5 psi

Ray Wohlfarth
Boiler Lessons

Comments

  • Danny Scully
    Danny Scully Member Posts: 1,463

    Negative. 15 PSI. See attached.

    IMG_6582.jpeg
  • Steamhead
    Steamhead Member Posts: 17,960

    Not a good idea to use MegaPress on steam, since it's too easy for the fittings to sag over time. And we know what that causes……………

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,533

    Bot PP and Mega Press are approved for low pressure steam up to 15 psi.