NFB 175H Thermostat

Options
bscott13
bscott13 Member Posts: 3
edited September 2025 in THE MAIN WALL
IMG_5593.jpeg

I recently had an NFB 175H boiler installed along with an indirect water heater. My question is about the installation: the installer connected the indirect water heater thermostat to zone three instead of using the dedicated DHW block. Zones one and two are used for my baseboard radiant heat. When I asked why it was done this way, the installer responded, “We prefer to pipe it as a heating zone because it simplifies troubleshooting in the future. We could have piped it directly off the manifold, but that can make it harder to diagnose a failure of the primary pump. That’s why we did it this way.” Does this make sense?

IMG_5595.jpeg IMG_5611.jpeg

Comments

  • 109A_5
    109A_5 Member Posts: 3,684
    edited September 2025

    Well, is seems it is more than just moving the two wires in your annotation, but not enough to avoid it. How does the boiler (or the system) control the water flow through the indirect water heater ?

    IMO doing it the way they seemed to have installed it (can't see the whole DHW loop in your pictures) you are loosing out of features the boiler has built in like DHW priority and maybe DHW temperature control by the boiler's user interface.

    I'm not sure I buy their explanation. So for ease of their (maybe future) troubleshooting you loose features and functionality, seems lame to me. They could close the isolation valves to the indirect water heater if that is messing up their troubleshooting strategy.

    Kind of seems like it is not piped per the instruction manual either (however I did not read the whole manual).

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    bscott13
  • 109A_5
    109A_5 Member Posts: 3,684
    edited September 2025

    Sorry, I did not see you added a picture, it seems Edits don't push the thread to the top of the queue or trigger notifications.

    It looks like they used a Zone Valve instead of a circulator for the DHW zone. Maybe a cost savings strategy on their part. If I understood the manual correctly. The way I believe the boiler is set up electrically (and logically) if you use the DHW thermostat input you need a DHW circulator. Since I suspect the boiler will not turn on the "Boiler Pump" or the "System Pump" circulators, it wants to turn on the "DHW Pump" circulator. (there are ways around that, but that just complicates things)

    It looks like the way they piped and configured the system, for you to have DHW the Boiler Pump AND the Zone 3 Pump (System) both have to be running and the DHW zone valve needs to be open. It may work but you probably loose the DHW priority and maybe other features and you are powering an extra circulator and a zone valve for your DHW.

    I would venture to say that is not what Navien intended.

    It seems when the DHW thermostat input is used it is the same as Zone 1 but with different features / functionality for DHW service.

    As far as troubleshooting (at least from a newcomers point of view) If you build the system different from what the manual shows that may add confusion, not making troubleshooting easier. Like a "not enough DHW" complaint in the middle of the Winter.

    image.png

    image.png

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    bscott13
  • JMWHVAC
    JMWHVAC Member Posts: 105
    edited September 2025

    No, their explanation doesn't make sense, and I still wonder, WHY would you do it that way? Do they have outdoor reset activated? If the settings are done right it will work but it is not the normal way of doing it. BTW, a good boiler you got there.

    bscott13EdTheHeaterMan
  • 109A_5
    109A_5 Member Posts: 3,684

    " WHY would you do it that way? " The only thing I can come up with save the cost of a circulator. And they were not even consistent with the placement of the Zone Valves.

    Made me think of something else, WWSD (Warm Weather Shut Down) Probably disabled. Another lost feature.

    No DHW above a WWSD set temp. Sadly too funny. Probably still disabled.

    image.png image.png

    If the Outdoor reset was enabled it may provide poor DHW temperature or extended boiler run time since the indirect's thermostat may never be satisfied. Since the boiler thinks it is a normal heating zone.

    image.png

    In this case, many pitfalls when you don't follow the manual. If you follow the manual and then if it does not work correctly it is not on you.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    bscott13
  • bscott13
    bscott13 Member Posts: 3

    Thank you, I appreciate your thoughtful review and comments. It sounds like the installation wasn’t done according to the manual’s specifications. I am not sure where to go from here or if it’s worth pursuing a change.

  • 109A_5
    109A_5 Member Posts: 3,684

    Few paths you could entertain.

    If you have not, you could read all the documentation so you understand your new boiler and all its features better. I'm not sure what your contractor obligated themselves to supply and install.

    You could see how it performs as is, DHW performance (especially when it gets cold out), fuel bills etc. If it falls short of expectations you now have a clue why. Is there a warranty on their install and for how long ?

    If the features like Outdoor Reset and WWSD (Warm Weather Shut Down) sound like features you would enjoy using and you enable them, monitor the performance, if it fall short complain.

    Maybe a bit late in this season for WWSD (Warm Weather Shut Down) activity but I bet if it was enabled, and is set for 70 degrees and it goes above 70 degrees outside you would loose the DHW heating. Maybe they never bothered to install the outdoor temperature sensor.

    Have a another contractor look at the situation.

    Many folks here on this site do their own work, not sure if that is an option for you.

    There are other routes if your not satisfied with the work the contractor did.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,749
    edited September 2025

    That depends on the leverage you have. Is the job paid in full?

    The outdoor reset feature of your boiler must be disabled in order for zone 3 to make enough temperature to heat the tank for DHW. If that was piped and wired in accordance with the manufacturers specifications, the lower temperature operation would save you on fuel usage for the life of the appliance, while the DHW zone would override the lower temperature for the DHW priority, and then the lower temperature would be restored to make space heating zones operate at a loser cost.

    If you have no leverage and you get pushback from the installer, contact the manufacturer and ask them if the instanned can be persuaded to resolve the problem. And there is always social media that can help. Ask me how I know this.

    Edit:

    As @109A_5 has indicated, you can set the system for the energy saving features but they may not work if there is no outdoor temperature sensor connected. Ask the contractor to connect the outdoor sensor so you can use the energy saving features the are listed in the manual. If they do not comply then ask for a refund for the inability to ues those features. If they are difficult, then start a social media campaign. I got results for a problem I had with handicap accommodations I booked 7 months in advance and with my less than 500 facebook friends, I got the hotel to solve the problem.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    109A_5bscott13
  • JMWHVAC
    JMWHVAC Member Posts: 105

    Your pic of the boiler wiring doesn't have the outdoor sensor wire on it. So apparently they skipped it. That saved them time on the install!😏

    bscott13
  • Kaos
    Kaos Member Posts: 851

    Get the installer back and have the wire properly with an outdoor reset and DHW on priority zone. As is, your boiler will probably run maybe 5-8 years before it dies an early death from cycling.

    How many linear feet of emitters you have in the place? A 175k seems overkill unless you are talking about a 6000+ sqft place.

    Work like this is why modcons get a bad reputation, the problem isn't technology but bad installation. They are not CI units and should not be set up like one.

    bscott13
  • 109A_5
    109A_5 Member Posts: 3,684

    Maybe some leverage here. Federal regulations violation.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    bscott13
  • 109A_5
    109A_5 Member Posts: 3,684
    edited September 2025

    Yup no wires there. And according to the manual the boiler comes with the Outdoor Sensor.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    bscott13
  • bscott13
    bscott13 Member Posts: 3

    The install was done about a week ago…The installer was very defensive about the DHW question. Says this is the best set up and easiest to service. There is not a separate circulator pump for the indirect hot water tank..they use a valve instead. Not sure if you can use the DHW features without the dedicated DHW pump? I’ll also be asking about the outdoor sensor.

  • Kaos
    Kaos Member Posts: 851
    edited September 2025

    The basic issue with the set up as is the boiler is set to supply fixed 180F water all the time. Besides the cycling issue this creates, this means it is not running in condensing mode and you are probably looking at around 85% efficiency. With proper setup with outdoor reset, you can get close to the nameplate efficiency number a good part of the year except for maybe a couple of cold weeks.

    That is real extra dollars you are spending on fuel that you should not have to.

    I don't know about this unit but some can use zone valves for DHW without needing an extra pump. This still needs to be a priority zone as you want hotter water than your house heat requires for fast recovery.

  • 109A_5
    109A_5 Member Posts: 3,684

    Often when intentionally taking shortcuts and then being 'Taken to Task' about them folks get defensive. Kind of Human nature.

    " Not sure if you can use the DHW features without the dedicated DHW pump? "

    I believe there is a way but it would involve adding a jumper wire and / or a relay. However I would recommend doing it as the manual recommends to maintain the warranty.

    Seriously, if it was done correctly would you be complaining ???

    " Says this is the best set up and easiest to service. " So he knows more than Navien ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 3,684

    @Kaos if you look a some of the diagrams (above) from the manual it appears Navien wants (or recomends) a circulator for the DHW loop.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 3,684

    " Says this is the best set up and easiest to service. "

    To me having circulators for more dedicated purposes may actually make it easier to troubleshoot.

    Example; No or poor DHW complaint, when piped correctly only one circulator is involved. If no space heat, probably not the DHW circulator.

    The way he has it, many more things (2 circulators, a zone valve, cold weather) could effect the DHW production, especially if the Outdoor Reset and WWSD are used.

    Maybe he does not understand that Boiler.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System