Viessmann vitodens 200 wb2 11-44 boiler problems
hello all I am having a problem where the boiler starts ,lights up,and shuts down right away
This will happen a few times and then it will light
There are no codes but viessmann manual says this symptom is due to flue gas system leaking
I have cleaned out in between radial heat exchanger with tool and flushed thoroughly with water
There is not a glue gas smell
Any help would be appreciated
Thanks
Brett
Fuel pressure ?
One Pipe System0 -
thank you I’ll check I have a manometer
Brett
follow up on my viessmann
Turned out to be the gas valve
Fortunately I bought a complete used boiler for $550 and had the spare part
Thanks for the help
Brett
Thanks for the feedback. With changing the Gas Valve you may want to have it checked with a combustion analyzer.
One Pipe System0 -
probably a good idea before I changed gas valve I changed the lgm29 board thinking that was the problem the board works but I notice it more short cycles itself to reach boiler temp limits and dhw settings
With original board in it would crank out on max to reach these settings now it kinda short cycles its way to the settings
I may put original lgm29 back it to see if behaves as it use to
I rember that I did not Mach up dip switch settings on replacement board so maybe that’s the problem
But am super happy it’s working now
I like this older viessmann it appears to be well built
Brett
yes I think you are right
this is the instlal sheet that would come with a replacement lgm29
I am pretty sure they still had an older form of what they call lambda pro today, on those boilers. so the gas valve is most likely non-adjustable. but you would want to make sure both units were set to the same fuel type. Also there is a water pressure sensor inside the unit which can shut it down if water pressure is too low.
1
- 15.8K Strictly Steam