Viessmann vitodens 200 wb2 11-44 boiler problems

bfriel64
bfriel64 Member Posts: 3

hello all I am having a problem where the boiler starts ,lights up,and shuts down right away

This will happen a few times and then it will light

There are no codes but viessmann manual says this symptom is due to flue gas system leaking

I have cleaned out in between radial heat exchanger with tool and flushed thoroughly with water

There is not a glue gas smell

Any help would be appreciated

Thanks

Brett

Comments

  • 109A_5
    109A_5 Member Posts: 2,737
    edited September 19

    Fuel pressure ?

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • bfriel64
    bfriel64 Member Posts: 3

    thank you I’ll check I have a manometer

    Brett

  • bfriel64
    bfriel64 Member Posts: 3

    follow up on my viessmann

    Turned out to be the gas valve

    Fortunately I bought a complete used boiler for $550 and had the spare part

    Thanks for the help

    Brett