Why purge valve above boiler? Pumping Away.

AlwaysLearning2024
AlwaysLearning2024 Member Posts: 55
edited September 18 in Gas Heating

Hi everyone!

Learning more about pumping away techniques and @DanHolohan writings and examples.

In one of this videos, he explains a simple way to purge the air from a single, hydronic boiler using a drain valve that is located on the supply directly out of the boiler. Curious why is specific location is chosen. Why not on the return side of the boiler?

I'm assuming this is so any air that may be in the boiler is also purged?

Thanks for any help!

Screenshot 2025-09-18 at 1.23.19 PM.png

Comments

  • hot_rod
    hot_rod Member Posts: 25,650

    you turn off the “service” valve , open the fast fill function

    So water can only go around thru the system, it pushes air as it goes, up through the boiler to the “drain” valve purge point

    With this method everything including the boiler gets purged from one point

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    AlwaysLearning2024HVACNUTclammy
  • HVACNUT
    HVACNUT Member Posts: 6,991

    The PRV enters the PONPC on the supply manifold when pumping away. Typically, the purge station(s) are on the return loop(s). If you follow the path of the water while purging, you'll see you never purge the boiler itself if set up that way. With a purge station as shown, you purge THROUGH the boiler.

    Drop the pressure before isolating. Having the boiler not protected by the extrol will blow the relief valve otherwise.

    AlwaysLearning2024
  • AlwaysLearning2024
    AlwaysLearning2024 Member Posts: 55

    Thank you, @hot_rod ! Is the circulator on or off during the process?

  • AlwaysLearning2024
    AlwaysLearning2024 Member Posts: 55

    Thank you @HVACNUT ! Am I dropping the pressure at the boiler fill PRV to something less than the expansion tank pressure (15psi) or simply monitoring the pressure to not exceed the boiler PRV 30psi because I’ve isolated the expansion tank?

  • hot_rod
    hot_rod Member Posts: 25,650

    Keep the pressure below 28 psi when purging.

    Or use a Caleffi 573, which is a high flow, fast fill valve, always. If you want to end up at 12 psi, set it at 12. It will flow about 5 gpm as it fills. No levers, screws, hoops to adjust, no worry about over-pressurizing.

    I keep the circ off while purging, dirt and air will be passing through.

    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Caleffi-573006A-Product-Overview.pdf

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    AlwaysLearning2024
  • AlwaysLearning2024
    AlwaysLearning2024 Member Posts: 55

    Thanks @hot_rod ! Currently the boiler has a Taco 3450. Would this be a suitable part for the job? Or is the 573 a better bet?

  • Big Ed_4
    Big Ed_4 Member Posts: 3,260

    It makes a neater job and simple to purge the system , one hose .

    Always makes me think of Dan's story of launching torpedos , Back in my Rite Fuel days, how many year . I am still launching them :)

    There was an error rendering this rich post.

    AlwaysLearning2024
  • hot_rod
    hot_rod Member Posts: 25,650

    I don’t have any experience with that fill valve

    If it is working, may as well keep it.

    If it fails, consider the 573.

    I do work for Caleffi, so….

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    AlwaysLearning2024
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,322

    Very simply...its the last spot before the unwanted air gets out in to the system. Mad Dog

    AlwaysLearning2024