home boiler replacement in spring, eastern Upper Peninsula MI

shambles
shambles Member Posts: 13

I'm having the asbestos taken out this fall (I think), and my 1962 Winkler with ca. 1975 Adams gas burner (hot water heat). Reality is I am far from any big city, so finding competent installer is a long shot at best. The one estimate I got thus far seemed like 'replace everything with what we sell even if it (e.g., circ. pump) is only 12-15 years old and works fine (we can't guarantee it'll work if we don't replace it').

Any general advice for those of us in the provinces?

Comments

  • mattmia2
    mattmia2 Member Posts: 14,136
    edited September 17

    It is normal to replace the boiler trim with the boiler, unless you have some complicated radiant system that is mixing a bunch of different temps or a bunch of zones and a manifold or something like that, if it is just a boiler heating some fin tube or convectors or radiators you would usually replace everything around the boiler. The labor to salvage, recondition, and re-install a couple hundred dollar part is going to be a wash.

    You're probably closer to Minnesota and Wisconsin than to people who know hydronics in Michigan.

  • offdutytech
    offdutytech Member Posts: 206

    You have to look at it from a contractor perspective. When I come in and give you a quote to replace your system and there's 1 or two pumps i'm going to include that in my price. I warranty the pumps, guarantee that the system works and provides to provide you heat when you need it. In the overall picture of the project it's a very minimal cost. If the customer asks to keep the pumps as a spare ok, no issue with that. If a system let's say has 10 zone pumps, yes that can add up and that's a different conversation. It's one where i'll give them the option for new pumps or keep the existing with the sign off that I can't be responsible for the existing pumps if there's an issue.

    Depending on where you are in the UP you might have to check south of the bridge. The Traverse City Area has some hydronics guys or maybe make a few calls to contractors in Marquette or even call Sid Harvey and ask for some recommendations they have a branch up that way.

    Are you looking for another cast iron or go with modcon boiler. If you post some pics we can better help you out. I can reach out to some suppliers here down state and see if I can put you in contact with a local or local ish hydronics contractor.

    Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.

  • shambles
    shambles Member Posts: 13
    edited September 18

    Thanks. Who is Sid Harvey? I've tried a couple places in the Sault, about 60 miles from me, only one interested. Ditto St. Ignace, same distance. One there was quite helpful on the phone, so will probably have them out (they'll charge for estimate which seems reasonable for the time), and got a reference for one in Marquette area (100mi.). Ideally I'd get at least 3…

    Here's a rough web page with some pictures:

    https://rjl.us/house/hydro-heat.htm

    The gas burner says '50-200,000 BTU, adjustable. A few online 'calculate your boiler size needs' websites give ~90,000 based on some combo of house age, footage, climate zone, insulation, etc.

    Ca. 1890 house, ~1800 ft2, blown-in cellulose wall insulation ca. 1985, attic insulated & vented properly, wood windows with wood storm windows and as I get to them, spring bronze weatherstripping. Solid & well-built. In a village (as opposed to on some windblown treeless mound like so many houses). I don't plan on ever moving, all house maintenance toward making it last another 130 years (boiler cost may hit the limit). I've done a lot to decrease heat loss in the 5 years I've been here. Normal winter lows are 5f a coupole 2-3x/winter, -10 or so for a day last winter. Usually only a few days too warm in summer, with combo of windows, shades, & fans (no AC).

    Existing setup heats house more than adequately, I usually have the thermostat down low & (if I can recall correctly) it only cycles on (burning) maybe 2-3x/hr; in other words I never have had to push it in 5+ years here (down to ~10f).

    I found a copy of 'form 1504h' but haven't done it yet, but have got sizes of all radiators, room sizes, etc.

    The circulation pump looks like it was replaced a few years before I bought the house; I believe it's more like a $1500 (or so) part… Of course they can't guarantee my gas inlet or radiators won't break either, but — you see what I'm saying? Or for cars: it's not normal to replace the control arm when replacing ball joints (or muffler bearings when changing tires). Would there be any need to replace the pump based on new boiler?

    I'm late 50s, not so well-paid US Gov field scientist (all the job threats & minimal retirement income associated) and can't imagine I'd have a spare $10k (in 2040 $ or otherwise) available to replace anything in 15 years, so guessing a cast iron boiler of ~85% efficiency vs. a more fragile modern 95% one is what I'd want, ideally.

    Got scared a few weeks back when I was trying to light the pilot on the speedflame (had it turned down thermostat since June, & turned off gas a few weeks earlier to replace kitchen stove), seemed like it wasn't lighting (no sound & didn't see anything ion the little hole) but after numerous attempts I just tried turning the thermostat up & it fired up normally, whew. So no hurry this fall but may as well get it done because not sure I'd be able to afford it at all in a few years (income, inflation, and economy).

  • offdutytech
    offdutytech Member Posts: 206

    Sid Harvey is a wholesale supplier for contractors. They have a good pulse on what companies do hydronic work. I've called up there to order some oil burner parts and were helpful.

    Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.

  • mattmia2
    mattmia2 Member Posts: 14,136

    is it all one zone? balancing those convector cabinets and cast iron radiators on the same zone will be very difficult.

    the circulator is an old 3 piece circulator. you could have replaced it with a much less expensive wet rotor circulator. probably not a bad idea to add a magnetic dirt separator to the new system with all the cast iron radiators and steel piping.

    unless you go with a mod con, which would work great on that system if you split the radiators and convectors in to 2 zones, you will need return water temp protection on the new boiler because of the mass of that converted gravity system.

    that convector inside the cabinet missing its cabinet isn't going to heat well, it gets its output from the convector cabinet drafting air through the elements.

    especially in the up you may need the pipe insulation in the crawl space to keep it from freezing.

    that broken cap is the cap to the curb box for the water service. it is a tube that goes down to the curb stop on the water service.

  • mattmia2
    mattmia2 Member Posts: 14,136

    the copper tube on the convector missing its cabinet is so that when that automatic vent inevitably leaks it leaks wherever that tube goes instead of under the cabinet.

    this one looks like it is sealed in a box where it isn't going to do much of anything, it has no way to pull air in and the chase to form the draft isn't tall enough

    Untitled Image
  • shambles
    shambles Member Posts: 13
    edited September 18

    Thanks. The pix are from when I just bought the house in 2020, posted question here as was new to HW heat, changed out a few of the ones higher on page for this question.

    .. So some lower questions I figured out, even though the village works didn't seem to care that there'd a hole in the water shutoff!, and those dusty little fin/tube rads were discussed then, incl. drilling holes in the wood of the one for convection; I haven't done it yet nor even screwed/glued it together properly, that bathroom's never too cold I guess or haven't gotten to it.

    I sure love the old iron radiators though (have added granite or marble slab remainders from the fancy counter place on top of most for shelves or Cat lounges. The ca 1940s in-wall ones are OK, though the ones that have to run through the crawlspace don't heat as high; I'm not having that asbestos removed & it'd be a pain in the arse to get to also to cover or repair with something extra).

    Also compression tank, not expansion (I bought DH's book)!

    All one zone; I 'discovered' last winter that if I keep the french door closed that separates the front door area & stairs up, the temperature not only stays a lot warmer down & not as hot up (= more even), but also lowered my 2-3 months of high bills from $400 to $300 (may be in part from adding window seals, etc. last year also). The area near the front door seems particularly poorly insulated, probably because of difficulty drilling & blowing in the cellulose back when (but door is properly bronze-weatherstripped!). So closing that door I guess keeps that cold from pouring in & displacing the downstairs hear up.

    Also should add that in normal winter evening of ~20-30f the circulation/heat may only come on once every hour or 3 or so at night when I turn it down a bit.

  • mattmia2
    mattmia2 Member Posts: 14,136

    the reason that the convectors don't heat so well, they heat and cool quickly so they want several cycles per hour, the cast iron has a lot more mass both in the iron and in the water inside so it takes linger to heat but radiates that heat for a while after the boiler shuts off so it wants fewer cycles per hour. if you either put the convectors on a separate zone or replaced them with some salvaged cast iron radiators it would be more even. the piping through the crawlspace really doesn't lose a whole lot of heat.

  • hot_rod
    hot_rod Member Posts: 25,651

    maybe @GGross knows someone up in that area

    There are competent hydronic folks in that area, many are small shops that don’t advertise

    Local plumbing/ heating wholesalers are a can be a source for referrals

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,038

    I ran my business that way. I never wanted to get into the conversation about "I just spent $$$,000.00 with your company and now you want to charge me to fix my thermostat because it was not included with the job"

    If you have zone valves that are 10 years old and a boiler that is 50 years old, you are getting the boiler, the zone valves and the thermostats that operate each zone valve. I would rather let my competitors deal with that customer. You get everything that could go wrong and we cover the entire job under the warrant and subsequent years service agreements. It is actually less expensive in the long run if you have one "old" part fail in the few years after the replacements job. Emergency service call fee, parts required shipping or pickup at supply house, return trip, actual labor time on the job, I get paid by you for all that extra expense that goes into saving some money on using existing parts. Especially if the part touches water and I need to drain the system to replace the part.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • GGross
    GGross Member Posts: 1,606

    Straits heating and cooling in St Ignace knows hydronics. I have known the owner of the company to drive to the lower peninsula to grab parts after hours for his customers, and from all of my dealings with him he is committed to doing good work.

    offdutytech