Installing circulator to boiler

kinghoward
kinghoward Member Posts: 23

External circulator to supply water to boiler in residence. Its a smaller Taco pump , one of the options recomme ded in the install manual. I want to mount the pump in an orange pex line either a foot away from boiler vertically, or three feet away horizo tally. I am concerned about weight on the pex pipe, I think its too much weight. I can build supports but any ideas or comments are welcome

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,914

    Use hard pipes or copper from the boiler to the pump location. That should be enough to hold the pump in place. Don't ever put a pump, or any other hydronic accessory like air scoops or flow check valves between 2 pieces of PEX tubing. It is not designed to support the weight of anything. You will surely see sagging and eventually develop a leak or even separation of the PEX from the fitting it is attached to, over time. Besides it looks so amateur and screams "I have no idea what the H*** I'm doing"

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2plumbworker
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,426

    Or use black pipe nipples on each side of the pump. Use split ring pipe hangers with 3/8 threaded rod with nuts and F & M plates (ceiling flanges) to mount the pump to something substantial

    GroundUp
  • hot_rod
    hot_rod Member Posts: 25,543

    A pump to supply water to a boiler? Circulator pumps mainly circulate water in a closed loop system. What type of boiler is this? Any pictures?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kinghoward
    kinghoward Member Posts: 23

    Hot_rod: Rianni residence boiler, there is no circulator in the boiler cabinet, so install manual shows an external pump going into boiler. Water comes from a spaced-T to the boiler then back to a loop circulating throughout the house. I hope this makes sense now. I forgot the model number, I beleive it is 90k btu boiler, condensing type. We are replacing the Weil McClain boiler.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,914
    edited September 1

    semantics. This post screams "I have no idea what the H*** I'm doing"

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 13,943

    do the near boiler piping in hard pipe, either copper or black iron. the fittings for pex will be very expensive and it will look terrible.

  • kinghoward
    kinghoward Member Posts: 23

    Ok, very good suggestions based on the topic. Much appreciated. Will post a pic when I am done. Take care. Thanks for the help!